I put two new spikes on a tt system and I am now getting a reading Ze-84ohms, I put new 30Ma trips on three boards but ,I am getting high tripping times on two of the RCD would this be the trips or would there be some other reason?
 
What is your Ze/Zdb readings at the incoming side of the RCD's in question ?

278ms and 327ms
? and were these the readings @ I delta n ?:93:
 
Last edited by a moderator:
Assuming BS EN 61008 or BS EN 61009 278mS is acceptable at I delta n. The 327mS isn't however.

Have the devices been tested in isolation?
 
What is your Ze/Zdb readings at the incoming side of the RCD's in question ?

? and were these the readings @ I delta n ?:93:

68 ,for give me ,I am just new to testing and I dont quite understand what you ment by,@ I n, in the test procedure .If you could reply and let me know ,that would be great. Another question out of the road.
 
When testing RCD's you should get 2 x 1n readings, 2 x 5n readings and 0.5 n readings

Have you got all 5?
 
Hi squat,

quote_icon.png
Originally Posted by spark 68
What is your Ze/Zdb readings at the incoming side of the RCD's in question ?

? and were these the readings @ I delta n ?:93:

I meant have you taken EFLI readings on the incoming side of the RCD's where your trip times appear to be high ?

And as Murdoch has kindly pointed out to you in the post above.

When testing RCD's you should get 2 x 1n readings, 2 x 5n readings and 0.5 n readings

Have you got all 5?

Cheers
 
68 ,for give me ,I am just new to testing and I dont quite understand what you ment by,@ I n, in the test procedure .If you could reply and let me know ,that would be great. Another question out of the road.
Hi squat, I delta n (in symbols I triangle n) is the nominal residual operating (tripping) current of the RCD, in this case 30mA.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
high readings on RCD test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
vbyrne,
Last reply from
vbyrne,
Replies
10
Views
3,130

Advert