I put two new spikes on a tt system and I am now getting a reading Ze-84ohms, I put new 30Ma trips on three boards but ,I am getting high tripping times on two of the RCD would this be the trips or would there be some other reason?
 
Assuming BS EN 61008 or BS EN 61009 278mS is acceptable at I delta n. The 327mS isn't however.

Have the devices been tested in isolation?
 
What is your Ze/Zdb readings at the incoming side of the RCD's in question ?

? and were these the readings @ I delta n ?:93:

68 ,for give me ,I am just new to testing and I dont quite understand what you ment by,@ I n, in the test procedure .If you could reply and let me know ,that would be great. Another question out of the road.
 
Hi squat,

quote_icon.png
Originally Posted by spark 68
What is your Ze/Zdb readings at the incoming side of the RCD's in question ?

? and were these the readings @ I delta n ?:93:

I meant have you taken EFLI readings on the incoming side of the RCD's where your trip times appear to be high ?

And as Murdoch has kindly pointed out to you in the post above.

When testing RCD's you should get 2 x 1n readings, 2 x 5n readings and 0.5 n readings

Have you got all 5?

Cheers
 
68 ,for give me ,I am just new to testing and I dont quite understand what you ment by,@ I n, in the test procedure .If you could reply and let me know ,that would be great. Another question out of the road.
Hi squat, I delta n (in symbols I triangle n) is the nominal residual operating (tripping) current of the RCD, in this case 30mA.
 
Last edited by a moderator:

Reply to high readings on RCD test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
297
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
531
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
781
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
569
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock