If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
So I have a job to quote for installing an outdoor sub main. It's in quite a rural location and the supply seems to be TNCS. However, there is another conductor that leaves the MET and looks like it could possibly go to to a rod (the cable that leaves through a hole just to the left under the meter tails) This might be part of the DNO's earthing if its end of line I guess.

I've measured Ze at 2.72 ohms. Where do you stand in regards to cable calcs? Obviously first port of call is to ring the DNO and see what their stance is on it.
However, if they are disinterested whats the best port of call? It doesn't seem right designing a circuit that cant meet disconnection times. I know TT installs we'd use RCD's to meet the requirements for fault protection. Would it be the same in this instance?

The covers are only off them henley blocks for testing purposes:p

tigers.jpg
 
Did you take a line to neutral loop reading.
 
  • Agree
Reactions: Marvo
what are you supplying regards the sub mains !
 
Does it drop down a pole before entering the ground and up to the cutout? Could be PNB if the pole has TX mounted onit.
 
  • Like
Reactions: Marvo
I couldn’t see where the pole was unfortunately. There was heavy greenery behind the existing meter cabinet which is externally located at the end of a track. I’ll nip up tomorrow and have another look as it’s not far from where I am working.

The sub main is potentially going to a steel frame around 160m away which will feed the rugby clubs new electric score board and from there it will potentially branch off to feed a couple of heaters in the dugouts and also a socket in a camera stand.

Overview.png
 
Last edited:
imo you should ring the DNO and ask them what system they have put in before going a head with the sub mains .
 
  • Agree
Reactions: suffolkspark
looking at the google map, TT from the DNO ? and then on to the sub main.
 
looking at the google map, TT from the DNO ? and then on to the sub main.
I'll ring Northen Power up tomorrow and see what they say. They are usually quite helpful. I would have thought the same apart from the earth entering the service head.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Rotherham South Yorkshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
High Ze Cable Calcs 20 characters
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
tomspark93,
Last reply from
tomspark93,
Replies
7
Views
1,828

Advert