I did a test on a domestic property today.
the Ze I measured was 0.60
this is above the maximum permitted that is 0.35 for a tncs system.
I coded it a c2 as the Ccu was a 17th edition dual rcd type.
do I have to notify the electrical supplier of this high reading? And have I coded it right?
any help would be very greatful. Thanks
 
Yes notify the supplier, code 2 is what I would code it as. Good luck getting them out for a high ZE they don't exactly put them as an urgent job.
 
Thanks
if they won't come out what do I have to do? Is it my duty as being the last electrician on site to get this sorted ASAP ?
 
Ask to speak to the duty engineer otherwise you'll spend an hour trying to talk technical to someone who doesn't actually give a damn.
 
it needs sorting. phone DNO and ask for the duty engineer. nobody else will have a clue. they have a duty to maintain the earthing at 0.35 or less
 
Thanks I will phone them first thing morning and hopefully get them out ASAP . Thanks again for above advice
 
I disagree, I has northern power grid out within 2 hours for high ZE on a TNCS. They treat it as an emergency call.
 
  • Like
Reactions: 1 person
Assuming the test leads and tester are ok? Have you confirmed the result with a second tester wouldn't want to look a idiot :wink_smile:
 
  • Like
Reactions: 1 person
Assuming the test leads and tester are ok? Have you confirmed the result with a second tester wouldn't want to look a idiot :wink_smile:

I agree always double check you tester and leads I use a socket in my garage to double check mine if get a high reading like that.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High Ze on TNCS
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
coxyboy,
Last reply from
Flanders,
Replies
10
Views
3,379

Advert