Discuss Home power intermittently tripping in the UK Electrical Forum area at ElectriciansForums.net

devion

DIY
Reaction score
1
Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no additional appliances were switched on or being used. There are times when it simply trips in middle of night when most appliances are not running.
There are also times when the trips can happen successively a few times in a minute but was able to recover after several resets.
So far am able to reset the RCCB all the time.

On few occasions, one of my MCBs also tripped & this helped me to suspect the issue could be isolated to one of my rooms. However in most cases only the RCCB trips, hopefully the occasional MCB tripping is not leading me to a wild goose chase.

With this, I had to switch off each devices in this room connected to the tripped MCB & monitor several days if trips been resolved.
Reading few blogs, MCB trips could be due to faulty appliance or overloading.
In this room, I have 3 PCs, 1 router & 3 handphone chargers plugged in into 2 socket outlets with 2 multiple sockets extension. I had this connection for several months w/o power trips which is why I am not suspecting overloading here.
In some instances of power trips during the nights, PCs & chargers are not in used, although power was not switched off for the chargers. Only the router is turned on all this time.
if faulty appliance, I would expect the trips would be almost immediate & not so intermittent.

Was hoping to find out any quick method to determine which of this is the cause of the intermittent trips other than isolating one each time & monitor several days.
Another suspect could be the RCCB itself although this would cost me to purchase a new one or engage a licensed electrician to fix it.
 
If the MCB is tripping then you potentially have quite a serious fault. I would definitely get an electrician in to look at this. Someone with the proper test equipment will be able to narrow things down.
 
Sounds like the MCB is tripping as well though
This was my initial suspect too as the fridge is the only high powered appliance turned on all the time. However the occasional trip on one of my MCB is not on the circuit of the kitchen. Is there a way to check whether the fridge is the culprit, it is 10yr old & I do see some sweating outside the freezer compartment, but this has been like that for past year w/o power trips.
Isolating the fridge is not a choice since I need to use it 24/7.
The intermittent trips makes it so difficult to pinpoint where exactly is the cause.
 
Can you use an extension cable and plug the fridge into a socket on a different circuit?
 
The intermittent trips still occurring, sometimes more than 12hrs apart w/o any additional appliances being used, with this am more likely now suspecting to be the fridge which is the only heavy loaded appliance operational all this while.
Only puzzling thing how it can be this intermittent as in several hours apart on the trips. Most of the trips also seem to happen during late into the wee hours, though day time does trip too.
Am thinking of getting the external power socket with a RCD, 13A Gfci Leakage Protection Plug on it to connect this to the fridge, so that if it is the cause, it will only trip this RCD instead of the entire house RCCB. This device is affordable instead of replacing entire fridge.
 
Last edited:
Prior to my new fridge which is a wait of 5 days, any idea how to overcome the regular trips during the fridge defrost heaters acting up? My trips are now abt ~11-12hrs apart which means the current defrost freq set is likely 12hrs. I was contemplating to turn the fridge power off for 60mins during those defrost cycles periods, whether this is advisable.
I was still hoping whether the external RCD socket will work though, so it only trips the fridge instead of entire house.
 
I’m afraid it’s unlikely an extra RCD socket will not also trip the upstream device too.
There isn’t much you can do that is practical in the meantime.
Does your cooker switch have a socket on it? An extension lead from that might be a temporary workaround.

Getting the normal leakage current measured or the RCD ramp tested would normally be the first course of action before replacing appliances. Or did you prove beyond doubt it’s the fridge?
 
Nope, my cooker hob is using gas. It is due to the frequent trips & the pattern that I have tracked which is very clearly that the trips occur around the ~12hrs intervals which I highly suspect its the fridge, which I read around that it has defrost times set at various intervals, some can be as long as 12hrs. My fridge is also >10 years old & some sweating seen at external freezer door, its about time to change anyways. Just that meantime, wat probable steps to take to prevent entire house to trip during the ~12hrs intervals.
 
I managed to locate the defrost heater unit at the freezer coil area, I simply terminated one of the wires & electrically wrapped it.
Let's hope this works.
Update, after terminating one of the defrost heater wires, my trips became more frequent. It is now every 3-4hrs compared to previous 12hrs. This is very odd....desperate to get the new fridge in which is 4 days time. My fridge I believed is auto defrost, dun see a timer circuit there, not so sure whether it is now triggering more regular defrost cycles...
 
Update, after terminating one of the defrost heater wires, my trips became more frequent. It is now every 3-4hrs compared to previous 12hrs. This is very odd....desperate to get the new fridge in which is 4 days time. My fridge I believed is auto defrost, dun see a timer circuit there, not so sure whether it is now triggering more regular defrost cycles...
You probably disconnected the Neutral. You need both cables off the element, and terminated in something safer than tape, can you trace them back to a pcb and unplug?
 
You probably disconnected the Neutral. You need both cables off the element, and terminated in something safer than tape, can you trace them back to a pcb and unplug?
Today I proceed to the circuit board & unplug the cables to the defrost heaters. Hope it works. Unfortunately, when I was doing this with the fridge powered off but the power plug is still plugged inside the socket, my main breaker trip!!! OMG, hopefully its the fridge & nothing else. All this while am suspecting the fridge......
If its not the fridge, my only suspect is the breaker itself....but the trips frequency is so random, sometimes with a pattern of ~12hrs apart & just yesterday, was very frequent, ~3-4hrs apart. The latest trip event 2x, was only 1/2 hr apart.
Really a mystery to solve if its not the fridge...maybe the RCCB has deteriorated after so many trips...>50 times since abt a week ago.

I contacted one of electrical company, after I told them its random & unknown root cause, he stated cannot engage them because they need the trip to occur when at the location.
Am sure more qualified electrician will be able to conduct some diagnosis of my household circuit to narrow down exact cause of the random trips.
let's see if disconnecting the defrost heater circuit will work. fingers crossed. At my wits end now, have to hunt down a good qualified electrician to remedy my random trips.
 
Today I proceed to the circuit board & unplug the cables to the defrost heaters. Hope it works. Unfortunately, when I was doing this disconnection, I powered off the fridge with the power plug is still plugged in, my main breaker trip!!! OMG, hopefully its the fridge & nothing else.
If its not the fridge, my only suspect is the breaker itself....but the trips frequency is so random, sometimes with a pattern of ~12hrs apart & just yesterday, was very frequent, ~3-4hrs apart. The latest trip event 2x, was 1/2 hr apart.
Really a mystery to solve if its not the fridge...maybe the RCCB has deteriorated after so many trips...>50 times since abt a week ago.

I contacted one of electrical company, after I told them its random & unknown root cause, he stated cannot engage them because they need the trip to occur when at the location.
Am sure more qualified electrician will be able to conduct some diagnosis of my household circuit to narrow down exact cause of the random trips.
let's see if disconnecting the defrost heater circuit will work. fingers crossed. At my wits end now, have to hunt down a good qualified electrician to remedy my random trips.
Unplug things when your playing with them.
 
Update - Been more than 10hrs with no trips, I conclude it is the fridge defrost heater causing the random trips. Ytd when I terminated one of the wires to the heater unit, I actually worsen the condition & experienced more frequent trips of 3-4hrs interval vs previous 12hrs. Read the manual of my fridge & it did state auto defrost every 4 hrs.
After disconnecting the defrost connection from the control board, the entire defrost heater is now terminated from the controls & power.
Thanks all to have provided feedbacks for my past 1 week plus ordeal.
Random power trips in middle of night w/o additional loads, trips in specific intervals of time, good lesson learnt here of what is the likely cause for such predictable patterns on trips. The one thing that confuses me was my bedroom MCB tripped occasionally & made me run a wild goose chase to start isolating devices from my bedroom. Funny that kitchen MCB did not trip where my fridge was.
 
I'm still intrigued by that bedroom MCB tripping.
I spoke too soon, tripped again at the 11th hour. Its frustrating now. Guess will have to engage professional service to investigate, probably wait after my new fridge arrives in 4 days time. Sigh...
One electrical company provided me standard package for basic checks, troubleshoot live out-going, circuit breaker trip/function test, short circuit test & water heater connections, additional charges if need to further isolate the root cause.
 
Yeah definitely need to get some testing done. Keep us posted.
 
Update - fridge was replaced & past 2 days no more random trips. Fridge was the cause but maybe not e defrost heater unit since I disconnected it from main circuit board, or maybe its still connected somewhere? Should have terminate e other end of the heater to confirm. Another interesting finding was even when fridge power is shutoff, it can still trip with the power cable still plugged in.
Suspect some residual current was still leaking after just turning off the fridge during e trip occurrence.
Lastly as in why my other MCB to bedroom was occasionally tripping, no idea on this. However this MCB is just beside the MCB connected to my kitchen where fridge was. Whether due to some kind of interference or something, it trips it. This one really blew me to a wild goose chase & doubting the fridge to be the culprit in the beginning stages of the frequent trips.
 
Wanted to update since my last one. After 3 days of no trips, it tripped again which concluded it was not the fridge. I continued to isolate individual devices in my room that had that occasional MCB trip during the frequent RCD trips, until one of my PC 750W power supply encountered an issue that my PC was able to power up & unable to boot up. After removing this PC out, no more trips observed for more than a week. Indeed it was one of my devices in the room causing this intermittent RCD trips.
Googling about earth leakage current causing trips, understood that it is the accumulative of leakage current of each devices that will cause the RCD to trip if it exceeds the limit. During my meddling with the fridge defrost heater, it probably caused more leakage current in my home circuit which then incur more trips & made me to suspect to be the fridge.
The lesson learnt here is that when isolating each device, need to unplug the cable from the power socket, the rogue PC that had been shutdown during times of trips made me not to suspect it to be the cause.
I was wrong about this.
A quicker method to check for high earth leakage current from each device is to use a leakage current meter & probe it with the live n
neutral wires of the device, & if the cable has an earth together with the live and neutral cables, need to exclude that from the measurement.
Saved some money of not calling an electrician to check. The PC power supply was RMA to the vendor as it is still under warranty.
 
RCD test, can elaborate more what is this? Can it done by my own or require license electrician?
Unfortunately, today my main RCCB tripped again, after 5 days!!! This time I managed to use my recent purchased GFCI power socket & then I plug my 2nd PC to this. Within minutes, the GFCI tripped w/o my mains tripping!!!
This GFCI socket actually tripped 2x when I turned on my 2nd PC connected to it, so I replace the power supply with a spare. Now am monitoring.
This is indeed very hard to determine with the longer intervals of a trip event but am subtly confident that am nearing a fix.

I did contact electricians & explained my issue, at least 2 of them stated that they cannot guarantee a fix but they can help narrow down the cause/s. They mentioned about mega ohm the circuit to check which I believed it is measuring the amount of leakage current in each circuit in my household.
Hopefully today's incident with the GFCI socket tripping on my 2nd PC is inferring the issue to be my PC, power supply or other components, this I might not know, at least I had the power supply replaced & monitor.
Very frustrating as it is very random & now becoming more sporadic & less frequent.
Am also hoping that the main RCCB is still fine, in case it gets much more sensitive to earth leakage after this many tripping...50x at least for now. I believed my RCCB is rated at 30mA, I googled the various RCCBs available out there, saw some which is rated at 100mA, not sure whether this is safe for household usage, which I thought can handle more higher leakage current appliances.
 
Last edited:
RCD test, can elaborate more what is this? Can it done by my own or require license electrician?
Unfortunately, today my main RCCB tripped again, after 5 days!!! This time I managed to use my recent purchased GFCI power socket & then I plug my 2nd PC to this. Within minutes, the GFCI tripped w/o my mains tripping!!!
This GFCI socket actually tripped 2x when I turned on my 2nd PC connected to it, so I replace the power supply with a spare. Now am monitoring.
This is indeed very hard to determine with the longer intervals of a trip event but am subtly confident that am nearing a fix.

I did contact electricians & explained my issue, at least 2 of them stated that they cannot guarantee a fix but they can help narrow down the cause/s. They mentioned about mega ohm the circuit to check which I believed it is measuring the amount of leakage current in each circuit in my household.
Hopefully today's incident with the GFCI socket tripping on my 2nd PC is inferring the issue to be my PC, power supply or other components, this I might not know, at least I had the power supply replaced & monitor.
Very frustrating as it is very random & now becoming more sporadic & less frequent.
Am also hoping that the main RCCB is still fine, in case it gets much more sensitive to earth leakage after this many tripping...50x at least for now.

A ramp test will determine at what amount of leakage the RCD trips at. It will need a proper tester to do this (either a dedicated RCD tester or a multi function tester)
 
Likely my final update. It finally got down to the PC PSU power cord causing the trips, but it was really weird in how this came about. I was using my PC with a replaced PSU connected to a GFCI power plug for few days w/o issues. I then head off to a week vacation & off mains power to this PC.
When I returned from my vacation & powered on this PC, my RCCB tripped immediately. I was dumbfolded. I was able to repeat this again & so its now very consistent that my PC caused this trip, but a week ago I was using this w/o issue.
When I unplugged the PSU power cord from it, I did noticed the end of the cord to have a tiny bit of liquid on it....tried to smell it but nothing.
I found another power cord & plugged this into this PC & there was no trip. Next I simply plug the problem power cord w/o load to a power socket, the moment I turn on the power, my RCCB tripped.
I tried to use a multimeter to measure the 3 pins of this cord but I was not able to read any ohms between them.
Dunno how this could have occurred, especially when this power cord was used fine a week ago & after powering off & a week later, this same cord had a catastrophic failure. How puzzling is this....some degradation of the cables within this cord?
What was that tiny bit of liquid found at the ends where it connects to the PC PSU?
I will try to cut open the cable to check for internal cabling issues. Maybe around the ends, might have some cable kinks that resulted in internal damages.
 
Thanks for the update!

Detachable appliance power cords vary in quality from excellent to nightmare, often with few visible differences to tell them apart as the bad ones usually have counterfeit approvals moulded in. They are often bundled with the appliance at a late stage by the vendor, and may not be of a quality that the OEM of the goods would approve. I have seen high-end professional media equipment costing $30k bundled with cords that did not meet the applicable regulations, because the global distribution warehouse purchased them separately to match the plug requirement of the destination country.

Problems found in defective and counterfeit cordsets include undersize conductors, aluminium instead of copper, out-of-spec plug pins, unapproved and non-sand-filled fuses, female contacts that are not correctly touchproof, reverse polarity, shoddy spot-welding and complete disconnects at the terminations, etc. etc. On this forum, we heard about a cord that was giving people shocks where the black plastic moulding of the connector body was partially conductive, presumably through contaminated plastic feedstock containing carbon being used in the moulding line. We have also seen a plug where the spot-weld tags were less than 1mm below the top surface of the plug and the slightest damage would allow them to punch through and be exposed.

Another cable manufacturing error that we saw causing intermittent faults was a mechanical splice, intended to draw a new length of conductor into the extruder, that had been allowed to run through and gotten into the finished cable, which cut through the adjacent core's insulation. Presumably they didn't even do a water bath test on the insulated core before making up the cable. I can imagine some constructional defect like this being responsible for your problems. It will be interesting if you are able to dissect it and find something definite.
 

Reply to Home power intermittently tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
604
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
382
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top