my niece has just moved into a rented property and found the db board under sink ,could this pass a periodic inspection report? see pic View attachment 2483

No this is not acceptable, the consumer unit does comply with the part ofthe inspection that covers being suitable for mutual detrimental influences, in this case water, it should be preferably moved or at least be up to a suitable IP rating
 
which is cheaper, move the sink or move the CU?
 
If a PIR should be carried out on change of occupancy, maybe you could ask the landlord if it was assessed as 'satisfactory' ?

well the regs state it does but do landlords know, the answer is no , having that dist board in that position is just one big no no ,the landord has to provide proof that the electrical installation is in a safe condition , in my eyes the installation should have RCD protection ,IQ i think you have made a good point, you are entitled to a copy of the periodic report , if you do get it i would get a second opinion too, because just looking at the position of the CDU rings alarm bells with me
 
Last edited by a moderator:
Yes, the position of the DB, the age of the 'next inspection' sticker and the lack of any rcd protection all point to the conclusion that this property hasn't been inspected in a good while.
Some landlords need a polite reminder as to their legal obligations and responsibilities.

Perhaps suggesting he/she takes a look at this publication might help:- http://www.esc.org.uk/pdfs/business-and-community/guidance-for/ESClandlordsGuide.pdf
 
Stumas have a read of the link IQ has posted worth a read , i was just wondering how the hell you get the fuse out of circuit 6
 
Last edited by a moderator:

Reply to inspection report in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
872
Hi all, Probs a simple one here but when testing a 3 phase board for ze as part of a periodic inspection plus part initial verification of a...
Replies
4
Views
1K
Hi I'm having some work done at my house and the electrician has said we need a full rewire. I'm a bit surprised given that we passed an...
Replies
33
Views
4K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
875
Hello, Does anyone know the requirements regarding the initial inspection and periodic requirements of domestic turbines? I’ve been told...
Replies
0
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock