Discuss Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Schoe1
Hi all i was wondering if anyone could shed some light on my problem. Came to test a ring circuit today L-L 1.23 ohms N-N 1.23 ohms E-E 1.98 R1+R2 0.73 then i did my insulation resistance tests L-N 500 ohms N-E 500 ohms then L-E 0.00. Nothing plugged in, only a few sockets connected the rest in junction boxes while the plastering is finished. Is there any obvious reason for this reading, how could i narrow down the problem? All the tests were carried out from the consumer unit.
Thanks very much
Chris
Thanks very much
Chris
500 ohms then you have a problem, any Neons, loads connected, or are you reading your MFT wrong? were you testing IR on the IR setting?
At a guess I would say that there are two different faults, the one causing the 500ohm readings and the direct short.
I say two faults as having a precise 500ohm reading twice is so extremely unlikely that it's almost certainly the same fault causing both.
Just follow the usual fault finding procedure of logical division of the circuit to find these faults.
It would be interesting to know what has caused the 500ohm fault though as it's such a precise round number and faults generally don't conform to such things.
Sent from my iPad using Tapatalk
Sorry Pete not sure what you mean, I was testing the Insulation resistance at 500 volts.
Don't know if it's me but your description of the readings you are posting are misleading, to help us/me help you, you need to be more explicit when describing your readings "I tested as 2 radials and got 0.00" don't mean a lot you have to admit, sorry if I come across as a git, but I don't mean to honest.
C'MON PETE, WHY BREAK THE HABIT OF A LIFETIME? :sleeping:
Sorry not a problem my fault. So the insulation resistance readings test at 500v
L-N = 500>megohms (reading fine)
N-E = 500> megohms (reading fine)
L-E = 0.00> megohms
Quickly split the ring circuit and tested as two radial circuits and on both radial legs I got the reading again of 0.00> megohms which i wasnt expecting. If there was a break in the cable i should be getting a reading on one radial circuit.
Reply to Insulation resistance problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...