Discuss Insulation Resistance testing of Emergency Lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
G
Guest 004
This is proving to be a pain in the backside. It just impractical to disconnect the emergency, as they are hard wired. So apart from putting notes on the test sheets, how can I get good readings, at present I am getting 100 ohms on all conductors, with emergency connected. When the emergency's were removed from the circuitry, readings were greater than 200 megs.
Any advise would be greatly appreciated.
IQ where are you:)
Reg 612.3.3 just do the test between lives connected together and the CPC. I know it is an initial verification as such, but your just the tester, and so I assume that is the only part of the EIC you will sign.
I would do it at 250v first and as it is an initial verification if you got good results do another at 500v. The 500v between LIVES-EARTHS should not cause you any problems.
Hi MrEnigma, I will do the same as Malcolmsanford suggested by putting the neutral and live wires together and test them against earth with the lamps in, first at 250v and then at 500v. I think you will get the right readings by this method. Hope this helps
Reply to Insulation Resistance testing of Emergency Lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
I have installed a circuit for an oven and carried out all of the relevant testing so far. Apart from a neon on the double pole isolation switch...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...