Discuss Insulation Testing Conundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
P
Piratepete
Hi Guys
Domestic - Old Hager Box 14 MCBs RCD Main Switch. Totally stuffed with wiring - not keen to disturb
Tested the Full L+N busbars to E. IR = 1.8 Meg b****r! So close to 2 Meg!
Tried L busbar to E -all trips off. 1.8 Meg!!!!!!!!! - had to disconnect RCD!
Tried each cct in turn L to E. Five of them reduce IR to about 1.8 Meg. Obviously a nonsence!
I'm theorising that one cct has a low IR Earth to Neutral and I'm seeing feedback through these other ccts which may have something connected/switched on.
Is the only way that I'm going to solve this problem going to be to disconnect the Neutrals one at a time to try and find a cct with low IR?
Cheers
Pete
Sorry mate if this is not what you wanted to hear, but you need to IR test each circuit separately. Remove or isolate all loads. Initially, test each isolated circuit one at a time with the neutrals commoned. Only if your results still suggest a common fault to several circuits would you need to separate the neutrals and retest.
Your 1.8meg, on the whole installation, is due to resistances in parallel. You will have to disconnect each circuit as stated earlier, and see what effect that has. With 14 circuits, my best guess is that if you do them individually your readings will come back into spec at 2 meg plus. If one circuit is low and pulling down your resistance total value, then you will find it fairly easily.
Cheers............Howard
Reply to Insulation Testing Conundrum in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A friend's partner has an interesting fault, if it is a fault. She sets the shut down timer on the cooker and when the timer goes off (which in...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...