I work as a Maintenance Electrician on Highways (not street lighting). I won't go into great detail but we have cabinets with DNO fuses and a meter then normally a two pole isolator. I've been doing this role for almost two years, We were transferred / Tuped across to another firm who tendered for the contract. One of the guys who has far more Network testing experience than me (though doesn't have 2391), was insisting a number of months ago that we needed to pull the DNO fuse (cutting seals) to get a true ZE and determine the Fuse rating. Up until then I'd been Testing ZE at the closest point to the meter with Earth removed to test towards the supply and noting the Fuse rating of the carrier (most are sealed anyway), generally the Earth is 16mm or 25mm and is two feet long so of negligible resistance. He still keeps insisting we remove fuses despite being told by hierarchy we should Not do this.

Who's right in this instance? We do have G39 BTW

Doesn't look as if your question been answered.

When testing for a Ze on a domestic property, I would take my reading from the incoming supply to the main switch of a CU. Unless I was replacing the tails, or had to isolate the supply using the main fuse, I would not cut the seal. Therefore I would not be able to verify the size of the main fuse. I would document what was written on the fuse carrier, noting I had not inspected the fuse itself.

Is there a particular reason, you need to identify the size & rating of the main fuse, in your case?

In my case my DNO allows Scheme members to remove their main fuse (with appropriate PPE), and reapply a temporary seal, provided by them and furnishing them with the details. Not all DNO's do though.
 
I work as a Maintenance Electrician on Highways (not street lighting). I won't go into great detail but we have cabinets with DNO fuses and a meter then normally a two pole isolator. I've been doing this role for almost two years, We were transferred / Tuped across to another firm who tendered for the contract. One of the guys who has far more Network testing experience than me (though doesn't have 2391), was insisting a number of months ago that we needed to pull the DNO fuse (cutting seals) to get a true ZE and determine the Fuse rating. Up until then I'd been Testing ZE at the closest point to the meter with Earth removed to test towards the supply and noting the Fuse rating of the carrier (most are sealed anyway), generally the Earth is 16mm or 25mm and is two feet long so of negligible resistance. He still keeps insisting we remove fuses despite being told by hierarchy we should Not do this.

Who's right in this instance? We do have G39 BTW

Ze is taken at the consumers supply terminals, this is the point at which the consumers tails connect to the suppliers equipment. This will either be the outgoing side of the meter or the isolator.
 
Ze is taken at the consumers supply terminals, this is the point at which the consumers tails connect to the suppliers equipment. This will either be the outgoing side of the meter or the isolator.
Not the outgoing side of the meter. That’s usually sealed.
Outgoing side of isolator if they have one, or supply side of mainswitch, or an accessible Henley if there’s no seals.

basically, if you need to cut a seal to access a terminal, you don’t do it.
likewise cutting a seal and pulling a fuse just to find out the size. If it’s not printed on a sticker, then it’s “not verified”
 
Not the outgoing side of the meter. That’s usually sealed.
Outgoing side of isolator if they have one, or supply side of mainswitch, or an accessible Henley if there’s no seals.

basically, if you need to cut a seal to access a terminal, you don’t do it.
likewise cutting a seal and pulling a fuse just to find out the size. If it’s not printed on a sticker, then it’s “not verified”

I'm used to seeing a lot of self connect meters, the outgoing terminals are not sealed and the meter has a built in isolator.
 
There's normally an Isolator at the top of our Local equipment and then a Block Terminal on a Din rail. So I never cut the seal to measure the ZE, just wanted others opinions as my colleague was insistent we should cut the seal and remove the fuse! I measure it from the block terminal as the resistance of the 25mm copper upstream is negligible especially as it's barely two feet long. If the measurement is too high then Isolator top then over to the DNO...
 
IMO you are right, and anyone suggesting that they "must" cut the seals to measure at the DNO terminals is just plain wrong (as well as acting both illegally and dangerously).
Firstly, as you point out, a couple of feet of 25mm2 cable will have less effect on readings than teh variability of the contact resistance of your measuring leads. Unless you were to employ precisions 4-contact measuring gear, then that few feet of cable reaslly is insignificant.
Secondly, we are normally measuring Ze (and Zs) so that we can calculate a maximum value for R1+R2 and R1+Rn in order to ensure correct operation of protective devices. If you are so paranoid as to want to account for those 25mm2 tails, then you need to include them in the calculation - and measuring Z at your main switch is the easiest way of doing that. So really, an insistence of measuring it at the DNO terminals is wrong in the technical sense as it's excluding part of the circuit from the measurements and calculations. Being pedantic, you could measure Z at the DNO terminals, then calculate the resistance of a few feet of tail, and add the 2 together to get Zdb
 

Reply to Interesting talk with DNO engineer in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
598
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
This is quite lengthy so get comfy... I had a bizarre call out relating to a job I attended about five years ago. The situation was they were...
Replies
11
Views
1K
We had a new supply installed this week. DNO installed new cut out and fuse externally. Meter operator sent his engineer to move the meter in the...
Replies
12
Views
2K
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock