Constant pressure springs - is that the term?
I’d say constant force spring
I work as a Maintenance Electrician on Highways (not street lighting). I won't go into great detail but we have cabinets with DNO fuses and a meter then normally a two pole isolator. I've been doing this role for almost two years, We were transferred / Tuped across to another firm who tendered for the contract. One of the guys who has far more Network testing experience than me (though doesn't have 2391), was insisting a number of months ago that we needed to pull the DNO fuse (cutting seals) to get a true ZE and determine the Fuse rating. Up until then I'd been Testing ZE at the closest point to the meter with Earth removed to test towards the supply and noting the Fuse rating of the carrier (most are sealed anyway), generally the Earth is 16mm or 25mm and is two feet long so of negligible resistance. He still keeps insisting we remove fuses despite being told by hierarchy we should Not do this.
Who's right in this instance? We do have G39 BTW
I work as a Maintenance Electrician on Highways (not street lighting). I won't go into great detail but we have cabinets with DNO fuses and a meter then normally a two pole isolator. I've been doing this role for almost two years, We were transferred / Tuped across to another firm who tendered for the contract. One of the guys who has far more Network testing experience than me (though doesn't have 2391), was insisting a number of months ago that we needed to pull the DNO fuse (cutting seals) to get a true ZE and determine the Fuse rating. Up until then I'd been Testing ZE at the closest point to the meter with Earth removed to test towards the supply and noting the Fuse rating of the carrier (most are sealed anyway), generally the Earth is 16mm or 25mm and is two feet long so of negligible resistance. He still keeps insisting we remove fuses despite being told by hierarchy we should Not do this.
Who's right in this instance? We do have G39 BTW
Not the outgoing side of the meter. That’s usually sealed.Ze is taken at the consumers supply terminals, this is the point at which the consumers tails connect to the suppliers equipment. This will either be the outgoing side of the meter or the isolator.
Not the outgoing side of the meter. That’s usually sealed.
Outgoing side of isolator if they have one, or supply side of mainswitch, or an accessible Henley if there’s no seals.
basically, if you need to cut a seal to access a terminal, you don’t do it.
likewise cutting a seal and pulling a fuse just to find out the size. If it’s not printed on a sticker, then it’s “not verified”