Discuss IR testing - results creep up! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
P
pencilpusher
Hi all
Why is it that on some circuit IR testing, the results shoot up to say 250 M ohms but then creep up towards a much higher value? I know that the results are OK, I just thought it may be some damp somewhere causing the problem possibly. Do you wait for them to stop creeping up or take a result after say 5-10 seconds.
Any views would be welcome.
PP
Not that many electricians do, but the correct way to record a IR value is after 1 minute, (in most cases). Which allows the test voltage to charge the complete circuit and find any weak spots in the insulation. A quick 3 to 5 second push of the test button, is not and never has been the correct procedure...
With otherwise good high readings I agree dampness can cause fluctuating readings, but a slow creep up I always thought this was due to capacitance effects, and thought this was the circuit just charging up.
With otherwise good high readings I agree dampness can cause flucuating readings, but a slow creep up I always thought this was due to capacitance effects, and thought this was the circuit just charging up.
Absolutely, a bit of capacitive coupling on long runs!
[/COLOR][/LEFT]
So one minute it is then, unless I get >999 M ohms immediately of course!
If I notice this, which I have in the past, I continue to keep the test button pressed in on my Fluke tester until it bleeps and enter the final figure displayed:thumbsup
Be thankful your not Hi Pot testing MV/HV cables (basically the same thing but at much higher voltages), that can be anything from 15 to 30 minutes, depending on if it's initial verification or for subsequent verification after an incident for arguments sake. As Hi-Pot tests are classified as a destructive test, often both test KV and times are reduced....
My experiences of pressure testing are a bit simpler lol,
IR test @ 1000V ,Hold trigger on the flash testing gun for 30 seconds, push 2.5kV AC through the switch gear for 30s, then IR test it all again @1000V. This was for simple type testing.
Edit: should have said for LV switchgear
Reply to IR testing - results creep up! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi Guys Looking to see if anyone has had the same issues. I went to a tennanted property last year where the house lights were flickering and all...
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...