Hi
i'm going to test some lightning protection tomorrow following on from some extra tape we installed. Im competant with testing the electrodes with the fall of potential method etc.
what im unsure about is the continuity testing, there are 15 down conductors, and i read on here that, using a fly lead to test between them is the method, with acceptable readings not exceeding 0.3 ohms.

can someone explain the exact method. do i test between every down conductor, because that would mean over 100 tests.

thanks
 
Hi
i'm going to test some lightning protection tomorrow following on from some extra tape we installed. Im competant with testing the electrodes with the fall of potential method etc.
what im unsure about is the continuity testing, there are 15 down conductors, and i read on here that, using a fly lead to test between them is the method, with acceptable readings not exceeding 0.3 ohms.

can someone explain the exact method. do i test between every down conductor, because that would mean over 100 tests.

thanks


It's a little bit more involved than that. Every joint/junction in the air network installation needs to be tested across, normally with a Ductor tester with at least a 10A current flowing into the resistance (0.1 ohm). Any test points in the down conductors need testing too, after reconnection, following the earth rod test on that down conductor.

A typical so-called low resitance ohm meter, that you find on MFT's and the like, is not suitable for carrying out any of these tests...
 
Last edited by a moderator:

Reply to Lightning protection continuity test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I'm new to this but stuck with an issue, so I'm looking for some help wherever possible. I have just completed a rewire, which I have a potential...
Replies
7
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock