might be in wrong section so be kind. got a warehouse/ fabrication unit with a mixture of 150w low bays and 250w high bays either metal a-xline or merc bulbs and 1x 400w son flood light. they are all on variouse phase. when they operate a 3 phase press machine or shut 3 phase door some of low bays plus the flood go off. not every time but getting worse. why. everything tight, insulations on all cables good, same voltage on all phases, drops slightly when machine / door used. any ideas, or is it a sign of the lights getting ready, been up about 15 years. any help.
 
depends on how low the voltage drops. below 220/phase could cause this.
 
The installation may have just been added too over the years with little regard to a proper design, yep sounds like volt drop to me
 
As above volt drop,try measuring voltage on lighting circuit then get someone to run a machine or open a door and see what it drops to.
 
I wouldn't mind betting those affected light fittings are the furthest away and/or have the most fittings on a circuit from the DB too?? lol!!

As Pete said, a common result of adding and adding again without taking in to account existing circuit design etc....
 
Can you get some photo's or do a drawing of this set up?

You're not going to get a good answer by feeding us dribs and drabs of information.
 

Reply to lights going off when opperating3ph door / machine in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, A lot about this fault confused me to be honest. So customer complained the doorbell was not working as intended. By that I mean the chime...
Replies
2
Views
676
Had 2 new lighting groups installed on a multi wire branch circuit that used to be used for kitchen outlets. The 12-3 cable enters the switch...
Replies
2
Views
815
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi all, I’ve got a question about an issue I’m having. During a kitchen renovation we’ve decided to have open doors fitted to the patio and as a...
Replies
2
Views
1K
We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock