Discuss Line to earth fault but MCBs will not trip..Why? in the Australia area at ElectriciansForums.net

T

timmy123

I was called to a single phase installation in a pub as the staff were receiving shocks when touching equipment such as fridges water pipes etc. I located a damaged cable where line and PE conductors were touching and causing 240 volts on the entire earthing system at the installation. In other words there was 240 volts PD between the casing of equipment/ water pipes etc and true earth. This was a TT system where the 100ma RCD protecting the whole installation had been removed at some point previously! The ZS reading I was getting was around 2 Ohms. The mystery to me is why none of the MCBs on the installation were tripping out?
I am probably missing something really obvious. Any thoughts/ ideas would be greatly appreciated.
Many thanks
 
What circuit was the fault originating from???

The only MCB's that would operate by themselves under fault condiitons with an earth fault loop impedance of 2ohms or more would be 6A & 10A, B&C type, and 16A & 20A B type.

The 2 ohms would be too high for any of the other to operate & clear the fault. Whomever removed the RCD is a total idiot that has risked the lives of ALL staff & customers of this pub.

I can only hope you rectified the situation AS SOON AS you found it and it isn't still in this condition!

If you look at the tables in BS 7671 you will see the max values for MCB operation under earth fault conditions.
 
With earth faults, there are those with negligible impedance, and those where there is an impedance.
The higher the impedance, the lower the fault current.
The lower the fault current, the longer the time a CPD will take to operate.
You don't mention what sort of device, or the rating of said device that was protecting the faulty circuit.
It appears likely that the fault had such a high impedance, that the current produced, was not enough for the device to operate.
 
Pesky things those RCDs, well they just keep tripping all the time, and the worst possible times, when the pub is full etc, after all it is only a small fault .....................best to get shot of them, and low and behold problem solved

I'll get my coat
 
Really boils my **** does this, it's exactly as you describe Mal, some incompetent fool has been in to have a look at this problem decided removal of the RCD was the easiest way out and left it at that.

It's a TT system for gods sake, might aswell just give him an MP5 and send him on his way!
 
it was proably done by someone who drinks down the pub. Yeah nmate, i know how to sort that out.
A decent sparks may well of offered a day rate to find the fault and rectify it, but this bloke just removed the RCD for the cost of or indeed a few pints!

I know a few blokes will moan at me saying this, but if we were to follow E54's advice and install decent earth rods with a stable low value, then this type of incident would be less likely to happen.
 
it was proably done by someone who drinks down the pub. Yeah nmate, i know how to sort that out.
A decent sparks may well of offered a day rate to find the fault and rectify it, but this bloke just removed the RCD for the cost of or indeed a few pints!

I know a few blokes will moan at me saying this, but if we were to follow E54's advice and install decent earth rods with a stable low value, then this type of incident would be less likely to happen.


Well thank you very much Johnboy!! lol!! You know it makes sense!! lol!!:hurray:
 
Well thank you very much Johnboy!! lol!! You know it makes sense!! lol!!:hurray:


i think most sparks know it makes sense, but when there is no specific advice on Ra vales, only very vague guidance, then most people see no reason to acheive low values, when an RCD is protecting the instalation.

Its also a matter of economics, as if say i was to quote £100 for just the earth rod alobne, and mr E. Lectrician from down tghe road only charges £20 for a rod, that the customer thinks does the same job, then who will win the work?
 
i think most sparks know it makes sense, but when there is no specific advice on Ra vales, only very vague guidance, then most people see no reason to acheive low values, when an RCD is protecting the instalation.

Its also a matter of economics, as if say i was to quote £100 for just the earth rod alobne, and mr E. Lectrician from down tghe road only charges £20 for a rod, that the customer thinks does the same job, then who will win the work?

I know the problems, ....and TT installations have never been cheap to achieve when done properly!! Even the other way round the problem, is expensive. ...ie, a CU with a 100mA front end S type RCD, with RCBO's protecting all the individual final circuits. At least you'll need 2 RCD devices to fail then!!
 
Still with a fault current of 230/2 = 115 Amps I'm surprised something didn't trip out.

Maybe the bloke down the pub has taken the MCB's out along with the 100ma RCD just for good measure.
 
Last edited:
Lenny,

Many thanks for your informative reply. The fault was located in a 16mm T/E cable supplying a second DB from the main DB in the installation. The second DB had a variety of 32/20/and 6 amp MCBs. None had tripped. No RCD on second DB. The main DB had a similar variety of MCBs. All MCBs are type B. No RCD on first DB. I resolved the problem by removing the supply cable to the second DB. The pub is closed and will be until a new supply cable is run to the second DB. Thanks again for your comments
 
Hi Spinlondon,

Thanks for your reply and the information about low/high impedances. many thanks.
The fault was in a 16mm t/e supplying a second DB from the main DB. Both DBs had a variety of type B MCBs but no RCDs. 6,20, 32 amp MCBs. The only RCD on the installation had been removed and it was a 100ma unit located at the DNO incomer point. The pub is closed until a new RCD is installed and a new supply cable from DB1 to DB2. DB2 has been isolated by disconnection the supply from DB1
Cheers
 
Lenny,

Many thanks for your informative reply. The fault was located in a 16mm T/E cable supplying a second DB from the main DB in the installation.

There we go then, large OCPD's need low loop impedances to disconnect under fault conditions which you dont ordinarily get on a TT system hence the requirement for an RCD.

Take that RCD away and..........
 

Reply to Line to earth fault but MCBs will not trip..Why? in the Australia area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
469
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I installed outdoor lighting and outlets. I finished this past year. I passed my inspection on April 2022. I was so pleased, BUT now the circuit...
Replies
3
Views
915
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock