Discuss Main Bonding issue. in the Australia area at ElectriciansForums.net
W
wcampbell
Hi all.
I 'm getting 1.58ohms continuity on this main 10mm Earth bonding to water. The bond continues up to the flat upstairs and who ever did the work threw in 12" length of 4mm earth for good measure. Am I missing something or is this a case of new E Bond. Fitted a new clamp but did little to reduce the figures.
Any thoughts please.
Thanks.
I think you have answered your own question in that the figure is too high and if it was 10 mm cable you would be looking at a lenth of 863meters.
You have already found a bodge job with the 4mm so IMO put it right by installing a new cable.
Hi all.
Thanks.
What a mess, hope that's the before picture!
Put in new separate 10mil bonds from where the water enters each flat to the respective METs.
Scrub the pipes to shinyness before fitting the clamp then test from the pipe to MET, what I was taught.
And use ring crimps.
Hi all.
Thanks.
Disconnect this cable to the upstairs flat, it should not be leaving your equipotential zone or be influenced/connected to/by another equipotential zone. As others have suggested, if required replace the bonding conductor back to the MET.
Just to be certain, why not check this water service, to see if it is an extraneous earth!!! might just be a section in plastic somewhere...lol!!!
Not sure if this comment helps but looking at the photo, it looks like the mains water supply is plastic.
Thanks all.
The pipe work is all metal apart from main incomer. Will replace main bond this coming week.
Then you need to do an IR test from the MET to the metal side of the water service pipe. If it's under 23000 Ohms (23 KOhms) it requires bonding, if over, then it's not an extraneous earth, and no bonding is required. But you'll still need to isolate/remove that bonding cable that is going to, or coming from the flat above....
Reply to Main Bonding issue. in the Australia area at ElectriciansForums.net
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Evening all, Recently started working for a company carrying out electrical installations - I've found a job today that didn't have any bonding...