Have a query regarding bonding for periodic.
1, Main protective bond for gas supply goes to the supply box outside the house, is this ok as would be difficult to connect it in the house close to the supply as it goes under the floor. If it is a problem what code ?
2, supplementary bonding below boiler 10mm (4 pipes all connected 10mm looks very neat with labels) but then goes into the a fused switch that feeds the boiler, so have a tight fit 1.5mm cpc along with 10mm going into the earthing connection. Is this ok, reading of the bonding to CU is still good 0.05 ohm, is this ok ?
1 You have within 600mm to make the connection but ideally, this should be done as close as practicable to the point of entry to the property (ie. the equipotential zone that you are creating).
2 Supplementary bonding at boiler positions is not a requirement of BS 7671:2008, you need to brush up on earthing and bonding regulations if you are carrying out periodic inspections.
i dont understand why you would come a fcu with a 10mm!, you want 2 make sure that the 10mm from the boiler is not the fcu means of earth i have come across that before
Reply to Main protective bonding and supplementary bonding, help please! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...