Reaction score
2
Hi, testing a UNI with one main supply, which in turn feeds around 10 separate building. Each building as it own Gas supply with meter, so therefore a Protective Bonding Conductor to each incoming supply. Does the size of the cable have to correspond to the incoming supply size, or to the size of the cable taken into the building. Also do all the bonds have to be taken back to your main earthing terminal , so right back to your main electrical intake point?

Hopefully ive made it sort of clear but im sure if i havnt your ask me something :(

Thanks
 
i'd bond each gas supply to the earthing terminal (EMT) in each building. what's the earthing arrangement?
 
Main bonding of ALL incoming metallic pipework/metalwork is required at each separate building whether the service has a meter or not. It is to be connected to the buildings MET, or as in this case it will be EMT's....

I'll await the answer to Tel's question about the supplies earthing arrangement to comment further...
 
Hi, testing a UNI with one main supply, which in turn feeds around 10 separate building. Each building as it own Gas supply with meter, so therefore a Protective Bonding Conductor to each incoming supply. Does the size of the cable have to correspond to the incoming supply size, or to the size of the cable taken into the building. Also do all the bonds have to be taken back to your main earthing terminal , so right back to your main electrical intake point?

Hopefully ive made it sort of clear but im sure if i havnt your ask me something :(

Thanks
a good question ,I would say it corresponds to the incoming supply,& not the size of supply cable,ie sub main.But very rarely seen.
 
Hi, testing a UNI with one main supply, which in turn feeds around 10 separate building. Each building as it own Gas supply with meter, so therefore a Protective Bonding Conductor to each incoming supply. Does the size of the cable have to correspond to the incoming supply size, or to the size of the cable taken into the building. Also do all the bonds have to be taken back to your main earthing terminal , so right back to your main electrical intake point?

Hopefully ive made it sort of clear but im sure if i havnt your ask me something :(

Thanks


The size of the bonding conductors to each building is sized on the origin of the installation ie the mains position. You can often find the bonding conductors to the various buildings are larger than there supply conductors.

Example
Supply to out building 4core 25mm swa. And where it's pme u may require a 50mm copper csa cable,for the bonds
 
Last edited:
Let's put it this way, depending on what size 4 core cable is being supplied to each of these 10 buildings, i hope you're not using the SWA as a combined CPC and main bonding conductor. It's fine to use the armouring as the circuits CPC, but not when it forms any part of a main bonding system... It's then either a 5 core cable, or run in a suitably sized separate green/yellow bonding conductor....
 
Let's put it this way, depending on what size 4 core cable is being supplied to each of these 10 buildings, i hope you're not using the SWA as a combined CPC and main bonding conductor. It's fine to use the armouring as the circuits CPC, but not when it forms any part of a main bonding system... It's then either a 5 core cable, or run in a suitably sized separate green/yellow bonding conductor....

Hi, thanks for the response. With guard the SWA as CPC and main protective bonding conductor, i believe that a separate CPC was taken to each building. Going back to the SWA as your main protective bonding conductor, i know your not allowed to used it for that but what regulation would you use? Thanks
 
Hi, thanks for the response. With guard the SWA as CPC and main protective bonding conductor, i believe that a separate CPC was taken to each building. Going back to the SWA as your main protective bonding conductor, i know your not allowed to used it for that but what regulation would you use? Thanks
544.1.1
Remembering that the equivalent conductance of steel is 8.5 times less than that of copper and so requires 8.5 times the tabulated csa.
 

Reply to Main Protective Bonding Conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
679
Incoming supply on our job comes into the building and then the tails from which go into a switched isolator with 200A fuses fitted. No idea...
Replies
5
Views
951
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
722
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock