I was putting additional sockets on a ring final circuit for a client - all done, pretty simple job.
BUT!! When doing the testing, found the main switch and live feed to main RCD had serious overheating damage!! Needless to say needs replacing! All the circuits are in good condition.
its an older MEM board 16th edition and I have managed to get a new main switch, the problem I have is getting the correct cable to replace the one on the board - these usually come with fuseboards - does anybody know where I can get one? Or should I just replace it with standard meter tails?
Post automatically merged:

I was putting additional sockets on a ring final circuit for a client - all done, pretty simple job.
BUT!! When doing the testing, found the main switch and live feed to main RCD had serious overheating damage!! Needless to say needs replacing! All the circuits are in good condition.
its an older MEM board 16th edition and I have managed to get a new main switch, the problem I have is getting the correct cable to replace the one on the board - these usually come with fuseboards - does anybody know where I can get one? Or should I just replace it with standard meter tails?
 

Attachments

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members

Midwest

-
Arms
Esteemed
Oh dear. You could try contacting Eaton. They took over MEM some time ago. They might be able to tell if someone has a stock of spares.

Otherwise, it’s a new CU.
 

Andy78

-
Mentor
Arms
Esteemed
They are usually a very fine strand cable with a treated end these days.
19 strand flexi tails may work well.

You can get kits by other brands but you'd have to verify size and length


You might need to consider if the regulation about manufacturer specific parts applies
 

Midwest

-
Arms
Esteemed
Personally, I’d steer clear of using other manufacturers kit. Might get messy; they’ve already nearly had one fire.
 

davesparks

-
Mentor
Arms
Esteemed
Clean the busbar with fine emery cloth, and replace the flexible link with a bit of tri rated (with ferrules of course)
 

telectrix

-
Mentor
Arms
Esteemed
Clean the busbar with fine emery cloth, and replace the flexible link with a bit of tri rated (with ferrules of course)
and replace the main switch.
 

Midwest

-
Arms
Esteemed
I’ve read before, that when any metal has been subject to thermal damage, it cannot be cleaned up and reused, specifically for electrical purposes.

And having taken on repairs, one takes on the responsibility. I would either replace the damaged items, or replace the CU.
 

freddo

-
Arms
Supporter
Esteemed
New board time, Memshield 2 is obsolete now so this is a good time to replace it with something current. Shame you didn't ask last week, I removed and threw out an identical board!
 

SparkySy

-
Arms
How soon if you could get spare did you need the link cables? I may just may have some spare if you can wait till the weekend I can have a look if it would help! I used to have loads of mem2 spares but down to the last few bits kicking around now
 
  • Thread Starter Thread Starter
  • #15
New board time, Memshield 2 is obsolete now so this is a good time to replace it with something current. Shame you didn't ask last week, I removed and threw out an identical board!
That’s a shame - it was only today though!
Post automatically merged:

How soon if you could get spare did you need the link cables? I may just may have some spare if you can wait till the weekend I can have a look if it would help! I used to have loads of mem2 spares but down to the last few bits kicking around now
ASAP sparkySy - I need to book in a return visit to repair properly. Let me know details if you have them. Thanks
 