Discuss Metal capping outside the 150 in the Australia area at ElectriciansForums.net
P
p11jor
Hi all just thinking when doing a rewire and running the cables down into the meter cupboard then these are never within the 150mm from edge, tomorow I am going to put metal capping over these, how do I connect a earth to this steel? Should I just run a 4mm from the earth block below?
Capping does not provide mechanical protection once it is plastered over. It is only used to stop the cables being damaged by the plasterers trowel! You could drill straight through capping and you wouldn't even notice. You install it with nails!
Isn't it in the regs though if your cable is not 150 from the edges or running inline with sockets and switches horizontal or vertical then steel earthed protection must be used?
I will have to check when I get my regs out.
Yes but the preferred methods of achieving this are by using, steel conduit, steel trunking, or a steel plate. I beleive the steel plate has to be min 2mm thick. Not too sure about the last point though. IMO, if it's difficult to pierce with a drill bit, then it's ok.
Sorry that's what I was getting at! So does this have to be installed to all the incoming cables above the meter cuboard if out of the 150?
Surely they will be "Clipped Direct" therefore visible and will also be protected with "Additional Protection" in the form of RCD's?
Failing that, ensure they are buried no less than 50mm in the wall :D
Or, just another suggestion, box the cables in???
No.... The consumer unit is like socket, left right up down is safe. You can see the cu! If you THEN find someone has drilled directly below above left right of it, well..... They're very very silly ....
Re plastered over - I agree with above so long as the tails are still visable why would that be a problem?
NO. The requirement is to install at a deapth greater than 50mm,
or use a cable which incorporates an earthed metallic sheath,
or earthed conduit or trunking,
or provide mechanical protection sufficient to prevent penetration of the cable by nails and screws.
or to route the cable in a safe zone and provide RCD protection.
There is no specific mention of earthed protection.
And as Spinlondon has said if cable is less than 50mm it needs rcd protection, if not rcd it needs mechanical protection, simples. Osg page 21-22 off the top of my head ;).
Also if clipped direct/visible no need to do anything.
Reply to Metal capping outside the 150 in the Australia area at ElectriciansForums.net
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...