Peeps,
I have been asked to run a supply for a single phase, 3.2a extract fan (systemair AW500E4).
Is it a requirement, recommended or just good practice to include thermal overload protection in such a situation?
Thanks.
 
I don't see your particular model in my catalogue so I can't give specific advice.

If the fan has a built in temperature protector, which from memory is usually denoted as S1 and S2 on smaller Systemair fans, it should be cabled back to the DOL starter and used as a trip.

If the fan is single phase and one of those that's hermetic where the bearings can't be replaced and/or it has non overloading blade characteristics ie backward curved centrif for example then I usually wouldn't include a thermal overload because by the time it trips the fan will already be scrap so it's moot.

If it was 3-phase I'd fit a thermal overload to cover against phase fail and voltage imbalance conditions.
 
This fan is likely to be under a DoI rather than a DoC therefore it will require integrating into a complete system, in accordance with the manufacturers instructions, if that requires overload protection then it will need that.
If it is being built into machinery then the requirements of the machinery regulations will apply.
If you are providing the supply, then surely you are terminating at an isolator and the fan controls are by others?
If not then you will need to build the controls in accordance with the relevant UK/EU legislation and likely the relevant standards such as EN 60204-1 for the controls, ISO 13849 if any functional safety is required, ISO 13850 if there are emergency stopping systems involved.
 
It's roughly 0.7kW (done off the top of my head). So above the 0.37kW threshold that BS7671 states a motor doesn't need OL protection.

It will need OL protection, if not already built into the unit.
 
Apologies, thought current was .32A ! But even at 3.2A would OL protection be necessary if appropriately protected with conventional fuse/circuit breaker ? Would most sparks think of including OL protection ? Rightly or wrongly (appreciate Rob,s post though) I,m afraid I wouldn,t.
 
Last edited:

Reply to Motor protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
715
I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in...
Replies
5
Views
821
Guys Need some advice please. I was asked last week to investigate a burning smell in a toilet turned out it was an extract fan one of 2 The...
Replies
3
Views
719
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
510
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
12
Views
361

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock