Generally, we would use the Wiska box. A couple of times apprentices have asked whether it would be OK to run a 6mm cable and join to the original ring mains in the Wiska. If the Wiska box is accessible for future R1+R2 testing, is there any reason this can't be done? My instinct is to say "don't" but I can't come up with a reason why (and it is true that a line of 6mm cables is neater than a clump of 2.5mm).
 
You might not like testing rings but that's not in itself a good reason to change the design; there are situations in which rings are superior, or perhaps I should say more specifically 32A circuits are superior to 20A and if it's in existing installation as a ring it has to remain a ring if one is going to keep the 32A OCPD.

If you have lots of small loads that are evenly distributed, 2x 20A gives an extra 8A in total to share out compared to 1 x 32A, and on an RCBO board the leakage is divided between two devices so possibly less risk of nuisance tripping. But you can't (or shouldn't) run 2 x 12A loads on either of the 20A radials, you've got to ensure one is on each circuit. You can run both anywhere on a 32A ring. Each configuration has advantages and disadvantages but the specific task of relocating a CU wouldn't normally involve an appraisal of those and reconfiguring the circuits.

Returning to the original point of whether it's acceptable to form lollipops, I would prefer not to. I can't see that it's a big deal to run a few more cables and the nuisance of having to test from two different locations isn't justified by the very minor saving in space and cost in the terminal box.
 
Easier to test two radials than a ring.
Also poorer fault coverage?

For example, many only do the R1+R2 test on a radial to verify (dead) that Zs will be met, and they should also check polarity at each socket as well. But you only know your worst-case R1+R2 if you also know the end socket, which for an EICR is unlikely. Though if you have just installed it then you would know.

If the radial is "pure" (i.e. only ever two cables at each accessory so no branching tree-like) then an end socket test gives you good coverage of the whole circuit, but in practice you might have a tree-like arrangement and so you have to test the "branches" to know that all are good.

Do you test RN+R2 as well? Probably not.

Where as for the RFC you are required to test all three: r1, r2, and rN and that gives you good knowledge of all circuit's connections are tolerably good from r1 and rN being practically identical, and r1/r2 ratio matching the CPC/L conductor size ratio (usually, assuming no metal bonding from more than one socket).

True, if there are spurs you do not have coverage of them in the end-end test and also for EICR probably no knowledge of where they might be, but when you do the socket polarity test using the figure-of-eight approach it gives you a very good indication not only of any possibly bad switch/contact in a socket, but also the likely existence of a spur from measured resistance not being identical to all other sockets.

Personally I don't like spurs for exactly that reason: they breaks the excellent fault coverage of the end-end test which is convenient to do at the CU without knowledge of the physical route and order of accessories.
 
Keep as a ring circuit

Not a big fan of Lollypop circuits

if the ring is not a ring a ding ding then may be consider 2 radials if you can't complete the ringer
 
radials are easier in virtually every respect.

You are part of a growing group.Visit this forum in ten years and you can be pretty confident you will be in the majority.

Again, being easier does not necessarily make something better.

A growing group of what? People who don't understand the advantages/disadvantages of all available circuit types? people who find rings too difficult to understand? People who can't cope with having more than one type of socket circuit to choose from?
 
Again, being easier does not necessarily make something better.

A growing group of what? People who don't understand the advantages/disadvantages of all available circuit types? people who find rings too difficult to understand? People who can't cope with having more than one type of socket circuit to choose from?
Just more dumbing down to accommodate the workforce, I guess.
 

Reply to Moving Consumer Units in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
838
I was just googling for skeleton boards after reading the last thread and various pictures of consumer units popped up, some wired terribly and...
Replies
6
Views
710
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock