Piratepete

The supply at a farm is 3 phase PME, currently with 2x60Amp and 1x100Amp cutouts. The 3 phase supply feeds via a 40Amp switchfuse to a board in farm buildings - the load seems to consist mainly of lighting distributed across the 3 phases. As well as supplying the outbuildings the 100 Amp leg is also connected to a 40 Amp spn workshop supply and the house consumer unit.

I have to get an 80 Amp spn supply to a remote bungalow (60 metres away).

I'm proposing an upgrade to the cutouts all to 100 Amp (DNO says ok), splitting the house, workshop and bungalow across the 3 phases to try to balance the load.

I have to install new tails - I can see that the 3 lives will be 25sqmm, but what should the neutral be? Answers to this and constructive comments to my masterplan welcome!
 
If the majority of the load is single phase, won't the return current be far greater than the 114 Amps that 25 sqmm is rated for? Ah! Just put brain into gear - it's 3 phase DOH!
 
Last edited by a moderator:
even if the majority of the load is 1ph, that will be balanced across the phases, and therefore cancel eachother out. if all ophases are exactly balanced, then the resulting neutral current will be 0A. in the worst case scenario, if all loads are on one phase, then the neutral current will equal the phase current. This is then no different to a single phase supply
 
By balancing the loads across three phases you reduce the net neutral current, providing they are evenly balanced.
 
Last edited by a moderator:
if all ophases are exactly balanced, then the resulting neutral current will be 0A. in the worst case scenario, if all loads are on one phase, then the neutral current will equal the phase current.
Surely the neutral current can only be zero if you're not using the neutral (all 380 volt kit connected line to line)? If everything is 230 volt using the neutral, the current will be max 100Amp because the return current is 120 deg out of phase on each line.
 
if all loads are on one phase, then the neutral current will equal the phase current. This is then no different to a single phase supply

Not sure if thats quite true. If your overloading one phase of a three phase supply, can't the neutral current be 1.73 times that of the phase. Which is why it's important to keep them as balanced as possible. On single phase supplies the phase current will be equal to the neutral because upon distribution its balanced. So if there 9 houses, 3 are fed from L1, 3 from L2, and 3 from L3, all sharing a common neutral back to the transformer, so in theory balances itself out.
 

Reply to NEUTRAL TAIL SIZE ON A 3 Ph SUPPLY etc? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
985
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
881
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
What can be worse than electrical installations on a farm, or in a pub?...... Chippys! Got a phone call from my local.... Lights and kitchen...
Replies
6
Views
821

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock