I have a potential customer who wants me to rewire hisgarage – existing install is in a bad state with a very old DB.
He currently has 2.no 2.5mm, 3 core SWA cables feeding powerto the garage DB (in a ring circuit) from a small DB (with RCD protection) nextto his main consumer supply. The distance between garage and the consumer boxis approx 50m.
The power requirements for the garage are: garage door,fridge/freezer, dryer and at least a further 3.no double sockets (foroccasional hand tool use), and a lighting circuit.
The SWA cables also feed 2.no outside sockets in his garden(one on each cable) - which are occasionally used for the electric mower /strimmer or pressure washer.
I have asked him to replace the SWA’s or install an additionalone but he is reluctant to do this as he has recently landscaped his garden andinstalled a new kitchen - the existing cables are run under floorboards /concrete in the house and underground in the garden.
I have carried out an insulation test on the cables and bothwere fine.
The supply to the house is TNS.
1) Would I be right in thinking that as the supply to thehouse is a TNS system, I could effectively make the garage a TNS system throughthe 3core SWA cables and I would not need to install an earth rod?
2) Would two 2.5mmSWA cables in a ring be ok to feed a DB inthe garage?
3) As the internal DB has RCD protection, would I be rightto only install MCB’s in the new garage DB?
4) If I was to get my work inspected at a later stage couldthere be any earthing issues or Regs which might not be covered by supplying aDB through a ring circuit?
5) I plan to install 1.no 6A radial circuit to lights and 1.no16A ring circuit for sockets and garage door.
Current carrying capacity of 2.5mm SWA (ref method D) is - 24ampsper cable, voltage drop approx 3% (per cable) so was planning for 32A RCBO (at houseDB) – any issue with this?
Sorry… I know I’m asking a lot, however I’m a new sparky andthis one is not straight forward!
Thanks
He currently has 2.no 2.5mm, 3 core SWA cables feeding powerto the garage DB (in a ring circuit) from a small DB (with RCD protection) nextto his main consumer supply. The distance between garage and the consumer boxis approx 50m.
The power requirements for the garage are: garage door,fridge/freezer, dryer and at least a further 3.no double sockets (foroccasional hand tool use), and a lighting circuit.
The SWA cables also feed 2.no outside sockets in his garden(one on each cable) - which are occasionally used for the electric mower /strimmer or pressure washer.
I have asked him to replace the SWA’s or install an additionalone but he is reluctant to do this as he has recently landscaped his garden andinstalled a new kitchen - the existing cables are run under floorboards /concrete in the house and underground in the garden.
I have carried out an insulation test on the cables and bothwere fine.
The supply to the house is TNS.
1) Would I be right in thinking that as the supply to thehouse is a TNS system, I could effectively make the garage a TNS system throughthe 3core SWA cables and I would not need to install an earth rod?
2) Would two 2.5mmSWA cables in a ring be ok to feed a DB inthe garage?
3) As the internal DB has RCD protection, would I be rightto only install MCB’s in the new garage DB?
4) If I was to get my work inspected at a later stage couldthere be any earthing issues or Regs which might not be covered by supplying aDB through a ring circuit?
5) I plan to install 1.no 6A radial circuit to lights and 1.no16A ring circuit for sockets and garage door.
Current carrying capacity of 2.5mm SWA (ref method D) is - 24ampsper cable, voltage drop approx 3% (per cable) so was planning for 32A RCBO (at houseDB) – any issue with this?
Sorry… I know I’m asking a lot, however I’m a new sparky andthis one is not straight forward!