...and of course it's nothing to do with the fact that physics laws changed and it became safe to use the neutral as the earth.

but just in case make sure theres a whopping great fat thick bond to the pipes that go in the ground. Just in case. Because it is safe really. Honest. Just kidding. Maybe.

It is, and always has been safe to use the neutral as an earth, when PME conditions by the DNO's have been met. It is, however an artificial earth. It may not be as safe in all circumstances as a TN-S earth, but still more than adequately safe in the majority of situations!!

The main advantage for the DNO is not having to provide expensive metallic sheathing or separate earthing conductors within the make-up of LV Network Distribution and branch off cables.

Oh BTW, the minimum main bonding conductors for TN-S installations should also be 10mm, ...eh, before you get to the contradictions that is!! lol!!
 
Must be not less than half the required size of the main earthing conductor and not less than 6mm?

What am I missing mate? Do I need to run and get my green book out of the van?
 
I don't either, but I don't mark it down if I do, I just do the calcs and even if it's PME I'd just check for signs of thermal damage, if none, note it and move on.

I'll admit a while back I was installing bonding out in the sticks, TT system, I got my roll of 10mm out the van and was immediately worried that I might not have enough so I did a quick calc (diameter of the coil x 3.14 x number of coils) and it came out at X meters. I then paced the run and remember thinking it'd be fine. I chanced it and failed big time, I was about a meter short! I then got my tape and measured the run to find my pacing was way out!

Solution?

20-30 mile round trip to pick up a roll of 10mm or do I just unwrap the brand new roll of 6mm I had bought the week before? Calc confirmed, second option won!
 
It is, and always has been safe to use the neutral as an earth, when PME conditions by the DNO's have been met. It is, however an artificial earth. It may not be as safe in all circumstances as a TN-S earth, but still more than adequately safe in the majority of situations!!

The main advantage for the DNO is not having to provide expensive metallic sheathing or separate earthing conductors within the make-up of LV Network Distribution and branch off cables.

Oh BTW, the minimum main bonding conductors for TN-S installations should also be 10mm, ...eh, before you get to the contradictions that is!! lol!!

hi E54,

yes, agreed, was being a bit facetious, it just amuses me thats all. I suspect the decision was based more on cost savings rather than "which was best" as in ...safest!

which leads me to suspect thats why they specify enormous bonding conductor csas to services for TNCS, so they have an incidental (!) backup earthing system in the event of the loss of Neutral, etc etc

call me a cynic.
 

Reply to Niceic in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
736
Hi Folks , Just looking for a bit of advice as I'm looking to get back on the tools so please bare with me if this is a bit long winded. I'm a...
Replies
1
Views
598
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock