graham123

100a tp mccb in main panel. 25mm singles suppying a db next to main panel. Length of the singles is less than a metre. Cables are in metalic trunking. Ccc of 25mm singles in trunking is 89a. This has only been installed 5 years ago. A C2 has been given on an eicr. I myself cannot see a problem because of the length of the singles. anybody else come across anything like this.
 
Graham there is every chance as you say of there ever being a problem with the installation.

I think though you are refering to the 3 metre rule in association with Reg 434.2.1 which is for fault protection and not overload

The EICR is flagging up overload and rightly it does not conform to section 433 and reg 433.1.1.
 
Its an MCCB More details regarding the overload device.
Time current characteristics, is it adjustable, how is it calibrated, what if any is its current limiting range.
What type of insulation is used on those cables and what are the operating temperatures.
How will those temperatures affect the disconnection times in relation to the operating temp of the MCCB and any heat transfer that may occur.
There could be more scope with those singles and its relationship with the device protecting them !!
The code 2 may or may not be justified, but with all the above taken into account the circuit could have been designed and calibrated for compliance.
 
Last edited by a moderator:
Check also the MCCB has not been derated, it is common for MCCB's to come with a adjustment dial.

Are the cables tri-rated?

Does the total value of OCPD's in the submain if full with no spare ways limit the actual current that could flow through the singles meaning the overload protection isn't required up front off the cables as the design of the install ensures the singles cannot be overloads.

If diversity has been used to calculate load and this is why the singles may be smaller then this on its own is wrong as you should not design systems with undersized cabling because diversity has been used the cables should be protected for times of higher demands where they may be subject to overload.
 

Reply to Ocp 25mm singles in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning, Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking...
Replies
22
Views
3K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
I have an older Crouse Hinds board with a 200A service. Due to recent rehab on the house, I found I have the need to install a sub panel. I...
Replies
1
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Evening everybody. It’s been a while since I’ve asked for the collective brains advice but this one has really got me stumped. I’ve been asked...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock