D

Deathproof21

Hi,
I recently installed 3 pirs in a stairwell in some offices to the spec provided (B.E.G luxomat 180/R as they are suitable for fluorescent lighting and 3-wire version), the lights would stay on continually and not go off, when ive broke the circuit down to make sure non of the units where faulty, all the pirs will individually turn the lights on and off as they should, but once they are wired together in parallel they wont go off. When ive tested the circuit, when the lights should be off theres still a voltage of 70-75v on the switch live... also when ive put my tester on to test this voltage there have been times when doing so will make the lights go off. B.E.G sent me supposedly correct suppression packs to cure this which i then found out where incorrect.

Has anyone had any similar problems with pirs or could give me some advice if im missing something blatantly obvious.lol, ive done all the obvious fault finding on them. They are wired straight forward the circuit supply and switch live to the lights is at one of the switches with a 3-core cable to the other pirs.

Thanks
 
Malcolms idea is good.
You haven't got permanent and switch lives swapped over between fittings?
Have you tried just two PIRs and see if this works, trying the combinations to see if there is one that is passing voltage when off.
Can you get the correct suppression fittings?
 
yeah the 5 lights have emergency packs, is it a back feed off them, i mentioned this to the guy i spoke to at BEG and he didnt seem to think it would have any effect
 

Reply to P.I.R's occupancy sensors in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
420
I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
8
Views
290
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
537
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
659
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
424

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock