Search the forum,
Discuss PIR coding help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
mcm
went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?
1. no earth connected to metal light fitting. earth in cable but not on light.
2. twin and earth cable in roof space. property being thatched roof no rodent protection.
3. no 30ma rcd protection to ground floor sockets. socket could be used outside.
4. no fan isolator in downstaires toilet. no window
5. socket over cooker. plug lead over above hob on double socket.
6. cooker cable not clipped to surface from isolator to switch.
7. no main earth bond on oil pipe.
The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property.
going back tomorrow so will find out what the electricity company say.
what codings would everyone say the points are.
thanks.
1. no earth connected to metal light fitting. earth in cable but not on light. code 2
2. twin and earth cable in roof space. property being thatched roof no rodent protection.not compliant with effect of externall influences, IMO code 4.
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. code 1 for outside sockets
4. no fan isolator in downstaires toilet. no window. isolator not obligatory. no code
5. socket over cooker. plug lead over above hob on double socket.code 2 IMO
6. cooker cable not clipped to surface from isolator to switch. unsure where you mean. code 4?
7. no main earth bond on oil pipe.code 2 if the pipe is metallic and comes from outside
The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property. see what they say. if no chance of pme, then you'll have to TT it
thanks.
my commentsa are my personal opinion and could be altered with an appropriate amount of the amber nectar
1. no earth connected to metal light fitting. earth in cable but not on light. Code 1 IMO
2. twin and earth cable in roof space. property being thatched roof no rodent protection. Possibly 4 but maybe just an Observation
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. Code 2
4. no fan isolator in downstaires toilet. no window No code
5. socket over cooker. plug lead over above hob on double socket. Probably no code
6. cooker cable not clipped to surface from isolator to switch. Code 2
7. no main earth bond on oil pipe. Code 2
thanks.
PIR codes Always opens up debate!!
true, but i stand on code 2 for the cpc not connected to light ( not a real and immediate danger), and code 1 or 2 for the socket can be used outside. we're mostly in agreement though.
I base my codes on the set ones givem to be by our companys I&T department, although I certainly see that the metal fitting presents no immediate danger, so I certainly wouldn't argue with a 2.
Sockets not on RCD I'm given the choice of putting 4, which I use where sockets are upstairs/unlikely to be used outside and 2 if they downstairs/near doors.
My personal favourite solution, which I have seen once or twice is stickers stating 'not suitable for equipment outdoors stickers' lol
1. no earth connected to metal light fitting. earth in cable but not on light. ( code 2)
2. twin and earth cable in roof space. property being thatched roof no rodent protection. (no code )
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. (code 4)
4. no fan isolator in downstaires toilet. no window (no code)
5. socket over cooker. plug lead over above hob on double socket. ( no code )
6. cooker cable not clipped to surface from isolator to switch. ( not sure what you mean exactly)
7. no main earth bond on oil pipe. ( code 2)
thanks.
cant see why sockets eithout rcd would be code 1 or 2 unless it is a TT
generally a code 4. however, if able to be used outside, i believe a code 2 is more appropriate because of the increased danger.
i'm not saying dangerous as in a code 1, but code 2 as requires improvement.
i would certainly recommend an RCD socket and state that in the comments.
but if i were a proper businessman like A.S. , i'd talk them into a full rewire at £20,000.
The bonding as your earth to me is a 2.
Light CPC is a 3
No RCD is a 4
T+E in roof is a 3
And is the no isolator in a TOILET or BATHROOM.
What I mean by non rcd sockets is the ground floor sockets could be used for a extension lead and lawn mower. The installation gas a 100amp 100ma rcbo switch.
the cooker has a double socket over the hob wich the hood plugs into. maybe a danger with lead over the hob.
1. no earth connected to metal light fitting. earth in cable but not on light. Code 2
2. twin and earth cable in roof space. property being thatched roof no rodent protection. No code
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. Code 2 (or code 4 100mA RCD is useful probably not a very bad shock)
5. socket over cooker. plug lead over above hob on double socket. Code 2
6. cooker cable not clipped to surface from isolator to switch. Code 4
The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property. Something you should discuss with customer first unless you have been told to do all remedial works, PIR is recommendation not action. Certainly a good idea but may well cost.
thanks.
Nothing requires further investigation so no code 3s.
Reply to PIR coding help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...