Hi folks, client has requested PIR on a property with disconnected supply (not sure how disconnection has been effected). Property has been empty for a long time and potential buyer (retired electrician - no pressure) wants to know as much as possible to see if price can be negotiated down.

Obviously can only do dead tests, but from a PIR paperwork point of view, any thoughts on how to handle? Client knows inspection, continuity, IR tests etc can reveal quite a lot.

Should I decline to do a PIR but do a basic inspection and give a written condition report, or do a full PIR as far as can be done (with lots of LIMS)? Clearly can't tick satisfactory but what goes next to unsatisfactory? LIM?

If method of disconnection was company fuse pull I'm inclined to put in a fuse and carry out full tests. Sound ok?

Many thanks!
 
Hi folks, client has requested PIR on a property with disconnected supply (not sure how disconnection has been effected). Property has been empty for a long time and potential buyer (retired electrician - no pressure) wants to know as much as possible to see if price can be negotiated down.

Obviously can only do dead tests, but from a PIR paperwork point of view, any thoughts on how to handle? Client knows inspection, continuity, IR tests etc can reveal quite a lot.

Should I decline to do a PIR but do a basic inspection and give a written condition report, or do a full PIR as far as can be done (with lots of LIMS)? Clearly can't tick satisfactory but what goes next to unsatisfactory? LIM?

If method of disconnection was company fuse pull I'm inclined to put in a fuse and carry out full tests. Sound ok?

Many thanks!

Do the full PIR with the limitation of 'no supply available, only dead testing carried out'

You CAN still issue a 'satisfactory' assessment based on the extent of your inspection/testing, just as you could with other limitations.

'The installation was assessed as being 'satisfactory' based on the limited testing carried out due to the lack of supply. Further testing is recommended on connection of a supply to confirm an effective earth, polarity, earth loop impedance, prospective fault current, RCD disconnection and function checks.'
 
  • Like
Reactions: 2 people
thats what i do with storage heater circuits - im not going back at midnight to do earth loop testing, R1+R2 is good enough with limitations for live testing :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PIR on property with disconnected supply
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
SW1970,
Last reply from
gooner85,
Replies
3
Views
1,994

Advert