Ive been to a job recently where I had 1 downlight at the end of a circuit start flickering several hours after its been turned on. It had a loose cable which I tightened and it worked fine for another few hours then started again. this time I checked the wiring to the other downlights. Didnt find anything wrong but it did work fine when I put it all together and re energised.
Several hours after I left it started again.
Ive check every light on the circuit. no problems, no sign of damage. have re energised and working fine again. been on for a couple of hours now.
IR test fine
r1 - rn = 0.87
1.5mm t and e.
Downlights have been incorporated into existing lighting circuit. several branches off the existing circuit each with 3 or 4 downlights on
total load of circuit 2.3a 6a type b mcb, rcd protection
Any ideas anyone?