Discuss RCD a but slow. Time for a change? in the UK Electrical Forum area at ElectriciansForums.net
Electron
I tested a customers BS4293 MEM 100A, 30mA RCD, which is about 25 years old, after it tripped overnight. The trip time at x 1 was 207.2, 78 and 54.2 ms at 0 deg. and 68.6 ms at 180 deg. I know that the limit is 200 ms, so one reading was slightly over, which is why I repeated the test. At x 5 it tripped at 50 ms at 0 deg. and 41.5 ms at 180 deg. So, again both over the limit of 40 ms. No trip at x 1/2.
Do these results mean I have to change the RCD? Or is there any tollerance? If so, can only get used identical replacement from the internet. Or should I change it to a RCD to BS EN 61008-1, like a Wylex 100A 2 Pole 30mA RCD?
If the RCD was tested with no interfering background leakage from connected circuits, then yes, it's failed the requirements of BS7671 and its product standard and needs replacing.
It is unusual for a 4293 device to trip and then fail under test with a meter. What range of MEM is it.
Are these some of the types that you can’t rely on tests conducted directly at the rcd terminals and need a couple of feet of cable?
When testing BS 4293 type RCDs the testing method is the same as normal. @1/2xIΔn on both + and - phases, the RCD should not trip within 2s. The RCD must operate within 200mS @1xIΔn on both + and - phases (Note this is shorter than the BS EN 61008 RCDs we are familiar with). On 30mA RCDs @5xIΔn on both + and - phases, the RCD should trip within 40ms.
If it's a BS4293 S type (time-delay) RCDs the testing method is a little different, first you need to select the RCD time-delay test mode and perform 1/2xIΔn on both + and - phases, the RCD should not trip within 2s, as normal. Followed by 1xIΔn on both + and - phases, there is a 200ms time-delay and 200ms fault time i.e. the RCD should trip within 201-400ms@1xIΔn. Most testers don't allow testing at 5xIΔn in this mode, so it is inhibited automatically, the result is not required anyway even if the test is performed.
BS 4293 RCDs have since been replaced by the BS EN 61008 types.
Type Test Current (IΔn) mA Maximum tripping time ms
BS EN 61008 X 1 ≤300*
BS 4293 X 1 ≤200
SRCD X 1 ≤200
All types for Additional Protection ≤30mA X 5 ≤40
Type S X 1 130-500 this should keep the op, happy. copy and put in the onside guide .
Does this help?
Does this help?
I wonder if it had been tested every three months for the last 25 years?
No. I always say to customers "Can I assume that you test the RCD's every three months?" They look at me as if they have broken the law!
Does anyone ever check the RCD? I only ever do it when someone pays me!
The only replacement you will get for that is from the used market, don't try to doctor in another non compatible device.
Reply to RCD a but slow. Time for a change? in the UK Electrical Forum area at ElectriciansForums.net
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K