I tested a customers BS4293 MEM 100A, 30mA RCD, which is about 25 years old, after it tripped overnight. The trip time at x 1 was 207.2, 78 and 54.2 ms at 0 deg. and 68.6 ms at 180 deg. I know that the limit is 200 ms, so one reading was slightly over, which is why I repeated the test. At x 5 it tripped at 50 ms at 0 deg. and 41.5 ms at 180 deg. So, again both over the limit of 40 ms. No trip at x 1/2.
Do these results mean I have to change the RCD? Or is there any tollerance? If so, can only get used identical replacement from the internet. Or should I change it to a RCD to BS EN 61008-1, like a Wylex 100A 2 Pole 30mA RCD?
Had your customer tested the RCD by using the test button? could be the mechanical mechanism had become tired or clogged up if no testing had been done.
 
WD40 might sort it, 1 way or another. faster trip times or BANG.:D:D:D.
 
There is a replacement RCD available for these Memera 2000 boards, but costs around £130 when I checked recently (EAM1002H, if I recall). In my case, I'm changing the board, rather try to maintain a board where half the circuits would still not have RCD protection.
 
Hi - sometimes they will come back into spec after "some exercise". Failing that, I'd be inclined to change it all out.
They might, but it's still not acceptable as they have already failed the test.

It's no use telling people to exercise the device with the test button several times before each time they have an Earth fault.

The device has failed.
 
They might, but it's still not acceptable as they have already failed the test.

It's no use telling people to exercise the device with the test button several times before each time they have an Earth fault.

The device has failed.
Although the device did operate recently, which is why it’s been tested.
 
Does this help?

No. I always say to customers "Can I assume that you test the RCD's every three months?" They look at me as if they have broken the law!
Does anyone ever check the RCD? I only ever do it when someone pays me!
Mine gets tested every time my other half decides to toast a tea cake and a current gets stuck between the casing and heating element!
 

Reply to RCD a but slow. Time for a change? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
888
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
764
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
548
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock