If there was a fault it could blow the DNO fuse even if you put 80A or 63A fuses in the SFI.But if there is a fault then either the main fuse or the isolator fuse could blow..
Discuss New circuit design question in the UK Electrical Forum area at ElectriciansForums.net
If there was a fault it could blow the DNO fuse even if you put 80A or 63A fuses in the SFI.But if there is a fault then either the main fuse or the isolator fuse could blow..
You have every right to be confused, as the regulations on it are a bit convoluted!Now I'm confused.
So you are saying that a fused isolator is required, due to the distance from the meter to the first CU.
What's the point in putting in a 100A fuse. We have always recommended a fuse lower than the main fuse size?
I don't believe you will be proven wrong, I've looked and looked and looked! The only two options I see I have is either terminal blocks in the DB (70mm in 25mm out) or the preferred option, reducing pins.I’m willing to be proven wrong but I think you’ll struggle to find an MCB that will accommodate 70mm and fits in a standard CU or DB. Most MCB’s I’ve seen only accommodate up to 25mm.
As for the run to the caravan point, yes you can run a 2-core SWA but you still need to earth the armour at the supply end but isolating it from the enclosure at the hookup.
If there was a fault it could blow the DNO fuse even if you put 80A or 63A fuses in the SFI.
They are, i have looked to buying ones on the larger side to help with the cable size. Is there an easier/better alternative?Are these single phase boards, 70mm? good luck.
How about using a branch joint to bring off some 25mm SWA that connected to your kiosk:They are, i have looked to buying ones on the larger side to help with the cable size. Is there an easier/better alternative?
If you expect 10A max or so then why a 80A MCB???I don't expect the load at any kiosk to exceed 10A, except for the last kiosk which will be around 40A I would suspect, but again, there may be more in the future (there is a barn close to the final kiosk which will likely want lighting and sockets in eventually.
I have decided to go for an 100A switched fuse after the meter. 100A main isolator in kiosk 2 and 3. With the feed from kiosk 2 down to 3 via an 80A MCB. Then from kiosk 3 to the final kiosk via a 63A MCB. All lighting circuits on MCB and the rings on RCBOs. At the final kiosk will be a 30mA RCD which will feed a future ring and lighting,it will also
I think they so a MS70 that might be better here for taking off a thinner cable, but not obvious on the usual suspect's web sites:How about using a branch joint to bring off some 25mm SWA that connected to your kiosk:
https://www.cef.co.uk/catalogue/pro...-resin-joint-kit-for-cables-up-to-70mm-4-core
A fault that is going to blow the 80A fuses is also likely to blow the 100A fuses you get no realistic discrimination . There's no point in limiting yourself further down stream by starting with 80A fuses.So because there may be a very slim change of the main fuse blowing with a 63A fuse in the SFI, then you choose to do no selectivity whatsoever... Interesting.... Not something I would do.