I tested a customers BS4293 MEM 100A, 30mA RCD, which is about 25 years old, after it tripped overnight. The trip time at x 1 was 207.2, 78 and 54.2 ms at 0 deg. and 68.6 ms at 180 deg. I know that the limit is 200 ms, so one reading was slightly over, which is why I repeated the test. At x 5 it tripped at 50 ms at 0 deg. and 41.5 ms at 180 deg. So, again both over the limit of 40 ms. No trip at x 1/2.
Do these results mean I have to change the RCD? Or is there any tollerance? If so, can only get used identical replacement from the internet. Or should I change it to a RCD to BS EN 61008-1, like a Wylex 100A 2 Pole 30mA RCD?
Had your customer tested the RCD by using the test button? could be the mechanical mechanism had become tired or clogged up if no testing had been done.
 
WD40 might sort it, 1 way or another. faster trip times or BANG.:D:D:D.
 
  • Funny
Reactions: DPG
There is a replacement RCD available for these Memera 2000 boards, but costs around £130 when I checked recently (EAM1002H, if I recall). In my case, I'm changing the board, rather try to maintain a board where half the circuits would still not have RCD protection.
 
Hi - sometimes they will come back into spec after "some exercise". Failing that, I'd be inclined to change it all out.
They might, but it's still not acceptable as they have already failed the test.

It's no use telling people to exercise the device with the test button several times before each time they have an Earth fault.

The device has failed.
 
  • Like
Reactions: 123
They might, but it's still not acceptable as they have already failed the test.

It's no use telling people to exercise the device with the test button several times before each time they have an Earth fault.

The device has failed.
Although the device did operate recently, which is why it’s been tested.
 
Although the device did operate recently, which is why it’s been tested.
It might have operated, but we don't know whether it operated within specifications.
 
Does this help?

No. I always say to customers "Can I assume that you test the RCD's every three months?" They look at me as if they have broken the law!
Does anyone ever check the RCD? I only ever do it when someone pays me!
Mine gets tested every time my other half decides to toast a tea cake and a current gets stuck between the casing and heating element!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD a but slow. Time for a change?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
Electron,
Last reply from
stevels4,
Replies
28
Views
5,376

Advert