Discuss RCD not tripping under test in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi all. New user, but have lurked around here and used advice in other threads before, but haven't been able to find this problem anywhere, so figured I'd register and give it a shot.

I've put in a new dual RCD consumer unit for a customer, went through all the testing with no problems, tested one RCD which was fine, then tested the other and it didn't trip at I. Out of curiosity, I tested it at 5I and it tripped in 9.4ms, then did the ramp test and it didn't trip (reading was >33mA). Figured it must be an RCD problem, so put the other one in its place and had the same issue. The one I thought was faulty worked without any problems in the other place, too.

I'm assuming it must be something in the wiring somewhere, but don't understand what would cause this, particularly as it does actually trip in good time at 5I. I may also just be very stupid, the unit was a nightmare to replace and I was a bit weary when I got around to the testing...!

I'm going back there at the start of the week to finish off, so would appreciate any help or advice anybody else might have who has had this problem before.

Thanks.
 
Last edited:
I had a guy ask me the same question before. He had a split load CU with 2 RCD protected supplies. Every thing was ok with the domestic loading and testing. He couldn't understand why the night time only supply didn't trip the RCD test switch during the day. He's a plumber now.
 
Hi
Lighthouse Phil, not very helpful! Have you had a bad week?

Manoworcs - IMHO your tests (swopping etc) do point to a wiring problem (though I'm not sure what would stop the RCD tripping - high Ze or Neutral resistance perhaps). Check your circuits, including the Neutrals

Pete
 
remove all loads from that side of the board, including neutrals. test RCD > if OK, then add each circuit, 1 at a time, testing the RCD each time. when it fails to trip, the last circuit added is the 1 with the fault. re=test that circuit.
 
Wylex board, both are 80A RCDs. Initially, I was testing it at the cooker outlet (in the same room), but tested at the CU when it didn't work. Disconnected the loads, but now it's been mentioned, I may have forgotten to disconnect the neutrals :mad2:

It was the last thing I was doing at the end of a tough week, so I'm blaming it on that. Cheers.
 
Wylex board, both are 80A RCDs. Initially, I was testing it at the cooker outlet (in the same room), but tested at the CU when it didn't work. Disconnected the loads, but now it's been mentioned, I may have forgotten to disconnect the neutrals :mad2:

It was the last thing I was doing at the end of a tough week, so I'm blaming it on that. Cheers.


I think you may be mis-understanding tel's post. His advice to disconnect the neutrals was as a fault finding measure. Tel was not saying that the neutrals should be disconnected as part of the usual RCD test procedure.
 

Reply to RCD not tripping under test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
375
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
919
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock