Discuss rcd to ring main commercial building (offices) dado trunking in the UK Electrical Forum area at ElectriciansForums.net
C
chopper
taking some trunking off the walls and fitting dado trunking and adding few extra sockets in. Does this require the circuit to be rcd protected.
the circuit is protected by a 32amp mcb .
all sockets in dado.
Lots of office machinery then, any thought given to the total Earth leakage? if the total Earth leakage exceeds 10mA have the sockets been installed as per figure 7.5.3(1) and 7.5.3(11) in the OSG regulation 543.7.1.203, 204 and 205?
Hi chopper..
From your recent history on here you qualified about 4yrs ago but were mainly testing domestic then you recently had a yr break to do telecommunication and now you back in the game... pls correct me if I'm wrong?
Looking over this you seem to have little practical installation experience and and especially any real knowledge outside domestic so I would recommend getting in with a comapny and gaining say 3-5yr hands on with someone to look over you as you still learning the basics, as has been mentioned this question you ask is a basic one in the realms of things and with your experience writing off jobs with testing and cert's I'm a little shocked you do not know the answer to this... also before asking why haven't you looked it up in the reg's as this is an easy to find regulation with a pretty much easy to interpret regulation - to note though as Amendment 3 is coming into force in a couple of months the exceptions to complying to these regs has altered slightly so ensure you have read and understood the latest version.
experience in domestic not installing anymore.if it was domestic I would use rcd or rcbo .not got a regs book . And I thought commercial in dado for IT equipment a mcb would be ok.
just asking a bit of advise
So how do you expect to install electrics to the regs if you dont have a copy?
The regulations BS7671 cover Domestic, Commercial and Industrial so a regulation thats are usually applicable in a domestic are the very same that are applicable in say Industrial, there are very few regulations that are specified to be only applicable to one of these areas so the general consensus is most regulations are across the board, the use of the Reg's book should be a regular event until you have a indepth knowledge of it and any ammendments that are introduced.
We are not attacking your character or competence here but do feel the nature of this question is a little basic to be asked by a practicing Electrician.
To help out you have been cited the Regulations you need to re-cap on and are relevent to your question.
If you are extending, altering or installing new then any of these points will have to meet current regulations regardless of when the previous was installed, in the case of your question then, you would be required to ensure your new sockets have rcd protection, now because the cables you install are within a dado system then the new cables are not subject to requiring rcd cover so a cheap solution is to fit rcd socket outlets. The alternatives are you fit front end rcd cover and then you will be subject to calculating design leakage from the IT equipment and probably dividing the ring into smaller circuits to spread the leakage between rcd's ...
We are happy to help but we need a sense that your trying to help yourself rather than just asking a direct question without showing what you think about the situation yourself.
In all honesty you come across as though you haven't got a copy of the regulations or have an outdated copy an are unable to reference the regulations yourself, as I said, its not hard to locate these regulations and they have been given to use to look up.
There are exemptions to fitting RCD cover on sockets but you should be avoiding trying to find reasons to loose personal protection of a circuit that usually requires an rcd and as the yellow book is redifining the how some of these exemptions are applied it also is trying to ensure dropping rcd protection has a very good reason.... I would suggest one good reason is a radial socket at home for a dialysis machine where a nuisance trip is actually more life threatening than keeping the afforded protection and in such a case I would also fit a T pin socket to ensure standard plugs don't get used in it.
Again the regulation of the requirements for standard sockets to be rcd protected is one that should be well and truely embedded in your knowledge, I can forgive not fully understanding the excemptions but thats not what you enquired about.
I would ask in your future threads that you attempt to show your at least referencing regulations - not understanding regs is common as many are ambiguous and thats definately what the site is about, giving info to members who consider the regualtions to be nothing more than a step to pass exams and can be forgotten after by using rule of thumb or tricks of the trade then this is not what we are about and will be clear if we feel you should be helping yourself more.
Note - you need the new regs anyway within 2 months or how you going to sign your work off as the Zs permitted values have now changed along with a good chunk of regulations some of which are slightly relevent to the question you posed.
You cannot be a competent practicing Electrician without a copy of the regulations in some format or other, I find it very hard to believe tbh.
I've been more than kind enough here to give you the direct answer but also advice I hope you take in :)
Ok cheers
I was a bit vague I do understand that new or alterations should be protected by a rcd but I wasnt sure of the exemptions. And with it being dado trunking and computer equipment .
thanks
The regs as they stand up until july did allow the ommitence of rcd cover if an instructed person was notified and aware, this regulation was very vague about exactly what was classed as an instructed person and it also got abused to giving unprotected circuits where really they should have been covered by rcd... now the new regs in force in July close all this ambiguity and explain exactly what kind of person said instructed person needs to be which means a lot of the practices of exemptions that have been occuring will no longer be acceptable with the re-worded or rewritten (depending how you view the changes) regulations.
To note here you need to check the earthing set up is compliant too with your ring main, it needs wiring with respect to having a functional earth set-up so if the existing doesn't and won't allow you to convert them then you could be changing all the sockets for twin earthing points sockets.
Reply to rcd to ring main commercial building (offices) dado trunking in the UK Electrical Forum area at ElectriciansForums.net
Doing some work in a commercial restaurant/kitchen the builders had already boarded and plastered the walls meaning my only viable route is to use...
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...