Geoffers

Hi folks,

changed a CU over yesterday to a dual RCD board. Standard affair, all tests fine. Did live tests, started doing the Zs for the lights. Both up and downstairs lights kept tripping the RCDs. I'm using my Megger with the 3 leads to avoid tripping. Megger was set to No Trip Loop and all that. Zs for all other circuits fine

Am i missing something? .......cpc's are all present and correct in all circuits as i thought initially i may not be getting a good earth.

Stumped
 
are the 2 lighting circuits on the same RCD, or 1` on each? is there the possibility of there being some leakage existing, so that the Zs test current takes it over the threshold? do a ramp test on the RCDs.
 
are the 2 lighting circuits on the same RCD, or 1` on each? is there the possibility of there being some leakage existing, so that the Zs test current takes it over the threshold? do a ramp test on the RCDs.

lighting circuits are on different RCD's ....good idea re ramp test
 
Did you try testing the RCD's to establish if they are goosed or not???

Unlikely but needs ruling out at least.

yeah, good point but as all other circuits tested fine i ruled this out, bit hasty perhaps....

i'll go back and approach with a fault finding head on ....

thanks all!!
 

Reply to RCD tripping on "No Trip" Zs test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
332
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
890
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
542
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
796
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock