ianphilip007

hi there

just been to a property too possibly extend a ring main (2 extra sockets). when looking at the ring circuit i noticed 2 fused connection units, on further inspection these were not spurred off the ring main but wired as part of the ring main (supply side) i assume they were once single sockets and have been replaced with fcu's for some reason.

is this still allowed as i have not come accross it before. appears to me to be electrically safe as it stands

any advice please
 
hi there

just been to a property too possibly extend a ring main (2 extra sockets). when looking at the ring circuit i noticed 2 fused connection units, on further inspection these were not spurred off the ring main but wired as part of the ring main (supply side) i assume they were once single sockets and have been replaced with fcu's for some reason.

is this still allowed as i have not come accross it before. appears to me to be electrically safe as it stands

any advice please

Perfectly fine, it's better than a spur if you think about it!
 
Yes nothing at all wrong with that. Reg 433.1.5 an accessory to BS 1363 may be supplied through a ring main and our spur most likely is a BS 1363-4
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
ring main advice (fused connection units)
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
nickblake,
Replies
7
Views
5,615

Advert