I've never come acroos this but I have just been reading that metal roller shutters which are connected to a motor should have main bonding as it is classed as an extraneous conductive part. Anyone seen this done ?
 
I would normally have agreed with you but it was an answer on the Voltimum Q&A site that suggested if the motor is not isolated from the shutter it should be bonded
 
Well I suppose that each installation must be judged on its own.
If the roller shutter is installed in such a way that it could become live then it should be bonded.
Otherwise I still say there is no need, the motor would be earthed anyway.
 
Hi all,

If the manufactures fitting instructions states the roller doors needs to be bonded then to comply with the 17th edition should it not be bonded :confused:
 
Our local fire station roller door is bonded to the motor the frame & roof runners are anyway, the door itself cant be as each slat is insulated with a rubber beading.
Noticed it today while putting in some cat5
 
if you wanted to bond it you could just do it to one of the angles or plates as its all metal. but ive never seen or done this in 5 years of fitting them
 
and if a Ford Transit becomes wedged in the door ( as they often do) bond that as well!
 
The shutters are connected to a steal shaft ,which in turn would be connected to the motors thus earthed throught the supply , the guides (not in the girl type ) would basically not cause a potential as there is no direct contact but loosly fits so any bonding may not nesseseraly work so id say it doesnt need bonding unless stated in the manufacturers installation instructions
 

Reply to roller shutter bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello Shop with a 100A main fuse LED lights few amps max, cash tills, cash machine, roller shutter, auto door, nothing pulling much power but...
Replies
6
Views
580
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
Hello Everyone, (NOT DIY JOB, Need advise prior to calling an electrician on site) Is it possible to swap a 3 phase rotary switch (roller...
Replies
2
Views
1K
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
329
I'm probably displaying my ignorance here, but fortunately I'm not one of those people who can't stand to be laughed at! I've been thinking a bit...
Replies
27
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock