Discuss running 25mm tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
B
bluecallum
Hi can someone tell me what the best way of running supply to cu from distributors supply if the run is more than 3 metres apart,as i have been told that you can only run 25mm tails no more than 3 metres,Thanks
If the run is more than 3 metres you run your tails into a KMF switch (isolator) and then your tails out of the isolator to the CU can be as long as needed.
well we protect it with a bs88 80A fuse, so when clipped direct we use 16mm (witha seperate earth) which will carry 85A before correction factors. What do you do then?
wait a minute, my mistake i should have said we protect it with a bs1361 type 1.
well those pictures are actually metal switch fuses. The term kmf is from an mem product number and now all similar non metal switch fuses are called a "kmf". This is what they look like.
www.alertelectrical.com/upload/pdf/753MEM800KMF.pdf
Reply to running 25mm tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...