Thoughts please?

Shed supply spurred off ring in house, ring is RCD protected.
SWA glanded into AD box outside back entry through wall into socket!
At the moment SWA feed just a twin socket, but customer would like a small CU put in with a few sockets & couple of lights.
Although i would like to see it have its own supply from CU the cost & practicality's of it would be difficult.
I cant see anything wrong with the existing supply being used, its a 3c 4mm SWA.
Dont want to try to make the customer go for a dearer option unless i can justify it on safety/regs grounds that its not acceptable as it is.
 
Personally I'd always have an isolation point between an existing socket and the "shed" supply rather than straight into the back of a socket.
 
  • Like
Reactions: 2 people
Personally I'd always have an isolation point between an existing socket and the "shed" supply rather than straight into the back of a socket.

Me too....load allowing bung an FCU next to the socket in the house......there is also the issue of load on a spur feeding a CU if you dont fuse it down,technically you could overload it ,and it wouldnt comply with the general requirements for a spur in app 15. ("an unfused spur should feed one single or one twin socket outlet only")
 
At the house end, take the SWA off a DP 13A FCU on the ring.
At the shed end, SWA into a DP switch, then through sockets to a 3A FCU, then on to the lights.
 
Last edited by a moderator:
  • Like
Reactions: 2 people
At the house end, take the SWA off a DP 13A FCU on the ring.
At the shed end, SWA into a DP switch, then through sockets to a 3A FCU, then on to the lights.

In this instance I think this is the best solution. If you use metal-clad either end, then earthing your armour is sorted without having to go through adaptable boxes.
 
  • Like
Reactions: 1 person
Looks like, for once, we all agree on the best solution.

Should we start to rewrite BS7671 to suit our common sense approach??

lol
 
  • Like
Reactions: 4 people
Looks like, for once, we all agree on the best solution.

Should we start to rewrite BS7671 to suit our common sense approach??

lol

Last thing we need now is someone to mention exporting the earth............DOH!!
 
hey thanks for your thoughts everyone, all posts noted & taken in & pretty much as i thought but wanted to double check, il be telling the customer & pricing for things to be done as per the general consensus of the post !
 
For what its worth if a client wants sockets and lights in a shed I'll quote them for a 2 way CU
 
Hey everyone, been reading up on the exporting earth situation & to be honest as something yet im not to have encountered previously (coming from a commercial install sprk background) id like to clarify the matter. It is a TN-C-S supply so therefore i am guessing i should be putting in its own earth rod & just use the phase & neutral & not connect the cpc the shed end just use it as a monitoring cable effectively to protect it via the house supply in the event of a fault on the supply going out the the shed but not for the install within the shed?
Surely the Zs reading will be far better & a far better earth path via the TN-C-S than the rod bearing in mind the built up environment the location is.
Sorry to seem a bit clueless, but as per alot of my posts recently i have just moved into domestic &its a minefield of things i didnt need to look at before. I am trying to learn more & take it all in but my mind is currently going into overload with it all lol!
 
No, you do not need an earth rod!
If there any extraneous parts, they'll need bonding back to the MET in 10mm.
 
  • Like
Reactions: 1 person
No, you do not need an earth rod!
If there any extraneous parts, they'll need bonding back to the MET in 10mm.

I was going to refer the OP to the Sticky covering this subject, ...But it seems as if this long running sticky has disappeared????
 
ok so no extraneous parts i.e wooden shed, just normal use sockets n lights will be ok
If it was a metal shed or container then 10mm(or bigger if conductor size was larger) back to MET, if this was not practical then resort to earth rod!
 
Change outdoor adaptable box for IP rated fcu (or an indoor fcu in an IP encosure)

terminate swa into metal clad twin socket (or adaptable box then on to plastic sockets)

Couple metal clad socket to metal clad fcu for lights

simples.

(unless max demand in shed is more than 13amps, then it'll have to get more expensive)
 
ok so no extraneous parts i.e wooden shed, just normal use sockets n lights will be ok
If it was a metal shed or container then 10mm(or bigger if conductor size was larger) back to MET, if this was not practical then resort to earth rod!

Basically, yes.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shed supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
craig1000,
Last reply from
Guitarist,
Replies
17
Views
1,823

Advert