Hi
Today I looked at a bathroom to do a renovation and noticed it had an electric shower with a 2.5mm T&E powered from a 13A FCU
Apparently this was tested and a cert was issued by an NICEIC electrician last month.
I'm relatively new to this but would have thought it would need to be at least 6mm up to 7.5Kw and 10mm for 8.5Kw
I can't think of any reason why anyone would fit it with a 13A FCU and 2.5mm cable?
Have I missed something?