Discuss Sub Board fed from a plug top, EICR Coding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I suspect it was done this way to avoid Pert P notification.

I also suspect the reason it is not mentioned in the regs is nobody in their right mind would do this (put a CU and related fixed wiring system on a 13A plug all the time), until Part P made it notifiable and costly for a non-scam person otherwise.
Desperate measures in this case.
Appalling design method.
 
Of course you can mention it but you will have difficulty putting a Regulation against it as it is outside the scope of BS7671.
110.1.1.i lists the domestic premises as being in scope.

110.1.2i lists circuits upto 1000 VAC as being in scope

110.2.vi alterations or additions to existing installations and cases where an addition of alteration would affect the existing installation, which would put it in scope.


134.1.1 Good workmanship & Considerations to manufacturers' installation ?

I can't see the manufacturer agreeing being supplied by plugtop as an acceptable installation method. We can argue HOW it is installed excludes it from 7671

There may be more but on a purely fundamental level you can argue it's inclusion in an EICR
 
Thanks again for all the responses. I’m back and forth with how to code it.

At the moment I’ve got it down as a C3 - reasoning being the 1.5mm cable is capable of taking 16A which is what the MCB is rated at, and there’s no signs of thermal damage.

Its a bad design tho, but that doesn’t really fall under my remit as long as it’s safe. Any current flow at greater than 16A would trip the MCB and it’s RCD protected too.

Am I wrong to keep it as a C3?
 
Thanks again for all the responses. I’m back and forth with how to code it.

At the moment I’ve got it down as a C3 - reasoning being the 1.5mm cable is capable of taking 16A which is what the MCB is rated at, and there’s no signs of thermal damage.

Its a bad design tho, but that doesn’t really fall under my remit as long as it’s safe. Any current flow at greater than 16A would trip the MCB and it’s RCD protected too.

Am I wrong to keep it as a C3?
It’s your call . your the inspector. having Read and participated in this post I’d say there Is more than one right answer.


The fact you’ve identified an issue is proof that you’ve done your job. Code it or don’t code it however, but I’d put an extra explanation on this one.

I won’t say I agree with the C3, but I won’t disagree if you chose to go to with that.
 
Thank you all for your inputs so far.

Is there anyone who disagrees with a C3?

The sub-board had 4 circuits:- 2 x Radial socket (each supplying one socket) 1 x Lighting (supplying 2 wall lights) and 1 x 20A air conditioning unit.
It is not a question with disagreeing. But are you one of an ever increasing group who feel they must code, and then a C3? Go on break the mould, dont code it.
Regards, UKPN
 
Thank you all for your inputs so far.

Is there anyone who disagrees with a C3?

The sub-board had 4 circuits:- 2 x Radial socket (each supplying one socket) 1 x Lighting (supplying 2 wall lights) and 1 x 20A air conditioning unit.
LI for ludicrous Idea hope that's spelt right
 
I think "proof" is the more appropriate word.
Regards, UKPN
The proof is outlined above (in the eyes of this person), not everyone will see it the same, that said we're talking a C3 and won't fail an EICR, so why are we discussing it ?
.
I look at it from EAWR Defence point should it go bad.

Judge; As the competent person what did you do to make the person ordering the works aware of the issue?

I'm not sure a footnote and the reasoning for not including it in the scope being 'its on a plugtop guv' would be much defense, a coded item on the other hand and a justification for inclusion in scope stating that issue and perceived non-compliance, would hold more weight.
 
It is not a question with disagreeing. But are you one of an ever increasing group who feel they must code, and then a C3? Go on break the mould, dont code it.
Regards, UKPN

I’m not sure if I’m part of an ever increasing group or not, but if I see something that isn’t up to scratch then I feel it’s worthy of coding. Especially as the wiring of the extension seems fairly recent.

A C3 won’t fail the installation .. just means it could be better.

If you wouldn’t code it, how would you justify that you haven’t?
 

Reply to Sub Board fed from a plug top, EICR Coding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
760
hi thank you for help in advance have a potential pv installation for a garage roof that is some 60m from the main house (main incomer in the...
Replies
9
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock