cliffed

-
Arms
Supporter
Reaction score
645
Installing Swa 35MM 4 c,to new school block.
This supply will come of a MPB,nearby,to me the supply to this MPB does not comply.
Concern once again are the size of the bonding conductors realative to the the Main REC supply.
The drawing we have,have no input on this, it’s a Tncs system,& earth bonding will be required.
In a nut shell, even @ this moment the supply does not comply,in my opinion.
Any thoughts,on this,once again Swa being used as cpc & bonding conductor.
 
The 35mm is inadequate to support main protective bonding. The minimum size for 10mm bonding would be 50mm four core.
 
The 35mm is inadequate to support main protective bonding. The minimum size for 10mm bonding would be 50mm four core.
The main bonding cable would be installed separately, the issue is the MPB
Best to write to the designer to highlight your concerns and ask for comments.

Also state that they will be designated as the "designer" on the EIC when you issue it.
on the case tomorrow
 

Reply to Sub main & bonding conductors in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
679
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
881
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock