SWA has a 3rd core for cpc as well as the gland earthing to the steel cab. why a banjo in a steel enclosure?
Because the steel you have drilled should not be relied on for an earthing solution(note in your set-up its a gland plate thus relies on self tappers as a fault path) the regs state a separate tail to be used, this is regardless of having a separate earth you still have to have an effective earthing of the SWA even if you have an additional core.
i see what you mean. i usually fit banjos and a tais as standard, just thought this job would not require, as armour is not used as cpc. paint has been removed,no need for rust prevention as it's in a dry environment. but will just bung in banjos and tails when back there wednesday. thanks for the heads up. been doing too much domestic lately.
OK ...i`m just going to come in at this point Dark..Because the steel you have drilled should not be relied on for an earthing solution(note in your set-up its a gland plate thus relies on self tappers as a fault path) the regs state a separate tail to be used, this is regardless of having a separate earth you still have to have an effective earthing of the SWA even if you have an additional core.
Consider yourself Dismissedi see what you mean. i usually fit banjos and a tais as standard, just thought this job would not require, as armour is not used as cpc. paint has been removed,no need for rust prevention as it's in a dry environment. but will just bung in banjos and tails when back there wednesday. thanks for the heads up. been doing too much domestic lately.
i see what you mean. i usually fit banjos and a tais as standard, just thought this job would not require, as armour is not used as cpc. paint has been removed,no need for rust prevention as it's in a dry environment. but will just bung in banjos and tails when back there wednesday. thanks for the heads up. been doing too much domestic lately.
This is why for the extra cost on these kind of installs, I bung in a length of 4" trunking, 2" bushed and earthed. Then I gland all my SWA's in, bolt through the banjo but no tail required.
R2 on each would confirm any chances of differing potentials appearing...Do you earth the armouring at both ends? I was told that you should because if you didnt and the unearthed end was terminated into an enclosure with other earths there could be a risk that they could be at a different potential.
OK ...i`m just going to come in at this point Dark..
Tel did mention about sticking a fly lead on them armoureds i glanded off into that panel....i said no...on the basis that its a steel enclosure....
so if theres any contravention here then i will stand and take fire for it....
no i know that.It was only brought up because its a gland plate Glen and not the main solid steel enclosure so would require a tail earth regardless of the separate core, don't get me wrong there was no intent to sound like I was taking a pot shot at his work but that aside I admire your honesty