Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective?

Went to look at a job and they want a supply to a pre wired Shepherds hut 50M away with no SPD as it has been sat unconnected for a couple of years.

The main incoming is entering an old barn that has a recent-ish Hager 3 phase board that is separate from the main house with its own meter.

So, the question is, do i need to somehow get an SPD on the single phase sub main in the old barn to feed the hut? Should i be replacing the existing mini 2 way garage board in the hut to incorporate an SPD at the use end?
 
Does the old barn have any equipment of value and/or that the loss of it would significantly impact on their business?

In terms of protecting the shepherd's hut then an SPD at the feed end of the sub-main is not terribly great as 50m of cable could pick up some energy if the strike is quite local. You would be better with an SPD at the its own garage board for protection of it.

Is it really just a 4-slot one so main switch/RCD and a pair of MCBs? If the sub-main is only 32A or so then you won't need protection for any SPD at the hut, or you can get an SPD that is OK to 100A sort of DNO fuse like the compact Wylex one.
 
I just noticed the BG do a 5-way pre-populated "EV CU" with RCD/MCB/SPD, in both internal and IP65 versions. Probably you would just need to change one of the MCBs for 6A for the lights.
 
Sorry for the reply delay!

No, there is nothing of value connected in the barn, just a few socket outlets and lights etc.

I think due to the sort of complexity I’ll skip it as you say, it wouldn’t be much help at the barn end and the hut has similar, a couple of sockets and a light so nothing of value.
 

Reply to New SPD Regs for Sub Main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Currently quoting for a job that needs to be done next week and working out how best to proceed, so thoughts welcome. Current situation: -->PME...
Replies
6
Views
4K
Hello guys new in this forum. In my 19 years as an electrician I've never seen this. Looking for any thoughts on this. Been asked to install a...
Replies
13
Views
4K
I have a problem with lighting protection in a charity in Zambia. The earthing is TT, i.e. earth pits or rods are provided for almost every...
Replies
10
Views
3K
Apologies for the complexity of this question, but there’s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock