E

egginyourface

Exactly what the title says. The tails have been run under the floor and chased inside a wall with no protection. What should i do?

Its a kitchen rewire and its nearly finished. Theres no switch fuse to isolate sub main only main cut out fuse
:confused:
 
the main supply and meter box are outside at the front of house. from there the the meter tails are run under floor boards and chased into wall directly to consumer unit.
 
I would suggest installing new tails from the meter and install a switch fuse in the meter box. Then if you can, replace the tails that are chased in with 16mm t+e.
 
The tails will need RCD protection if they are buried in the wall.

Anyway cant you run them surface in trunking?

If not its either steel conduit or SWA.

:)
 
i wouldnt use twin and skin, unless you use an s type30mA rcd, or its 50mm below the surfaceor buried under earthed metal. SWA is a good alternative
 
I didnt think tails had to be on an rcd? Best thing to do would be what jason said and use swa out of a switch fuse in the meter box. You do need a point of isolation between the meter and the consumer unit if the distance is more that 2M from the cutout.
 
its a time delayed rcd. it is used to provide discrimination with RCD's, as the times 3 rule doesnt always work, according to the more experienced blokes on here.
 
I didnt think tails had to be on an rcd? Best thing to do would be what jason said and use swa out of a switch fuse in the meter box. You do need a point of isolation between the meter and the consumer unit if the distance is more that 2M from the cutout.
they dont if theyre on the surface mate, but if theyre buried, and a dont comply with the 50mm rule, or protected by earthed metal, then an RCD is a viable alternative

agree with the over 3m rule
 
its a time delayed rcd. it is used to provide discrimination with RCD's, as the times 3 rule doesnt always work, according to the more experienced blokes on here.

Never seen an rcd installed before the cu on new installations. That massave site in canterbury has meters which feed 80a switch fuses. Out of those goes 16mm t+e which has runs in excess of 4 meters, but NO rcd fitted until youget to the cu.
 
Fit a KMF switch fuse at the meter cabinet end and expose the buried tails
Then either surface trunking, or plate them with a suitable metal strap, otherwise you cant avoid having Rcd protection for the buried cables
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
submain 10 mtrs away from main supply run in tails
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
egginyourface,
Last reply from
malcolmsanford,
Replies
27
Views
4,163

Advert