The 115A rating for single phase armoured cable is for 90°C cable and means the cable must be installed in such a way that the conductors can reach 90°C; it is not likely that this is practical to do, therefore even if the cable is rated at 90°C the limit on conductor temperature is 70°C therefore the cable can only carry 97A.
Too many other factors to cover to be able to say if the installation is safe.
 
Sorry if this is not the correct wat to post my query, I am new to the site. I am not a spark but would like to tap into the skills and experise on here before I set off on the wrong course with my current spark. I am having a garden office built, it has had its own CU installed but my ex spark neighbour came round to look and has caused a row with my spark by saying he was incompetent and had done it wrong. I'm confused and don't know who to believe.

The new cu is fed from house via a henley block with its own 100amp isolator. The CU in house is on a mains fuse of 100 amp with 25 mm tails.
The issue is the cable used to the garage, it is free to air, 15 m long and swa 16mm 3 core cable. 1 of the cores has been used as earth, so my spark says its 2 core single phase system which can carry 115 amp.

The room will sometimes draw 70 to 80 amps as has an electric 9.5 kw shower, sockets and lights.

My neighbour ex spark has disagreed and says 'in his day' it would be on 25mm cable. Is my house in danger or is my spark complying with current regs?

Change the iso for a switch fuse and have a 63/80A fuse in it. Likely to be fine then (without further info (TT supply maybe, etc, etc)). As mentioned it is highly unlikely to be drawing 70-80A unless the police helicopter has spotted something on their thermal imaging cams!
 
was just thinking the same. a KMF fused at 80A. just doing a similar but with 10mm SWA fused at 60A. however, i hate the wylex KMF. it's designed for incomer at bottom, and there's no way to have incoming cable into top feeding the bottom of the isolator. next option up from the GC MSF