Not always, a Double pole or a TPSN/four pole isolator isolates the neutral.
And most plug and socket arrangements used for isolation will isolate the earth.
our 4pole isolators early make, late break

have a seperate earth and n connection as well mate.

buy a different brand then mate
 
  • Like
Reactions: 1 person
our 4pole isolators early make, late break

have a seperate earth and n connection as well mate.

buy a different brand then mate

Why would you need a seperate N in a four pole isolator? That's what the fourth pole is there for!

And I am quite happy with the brand if isolator I use, MEM are tried and tested.
 
Why would you need a seperate N in a four pole isolator? That's what the fourth pole is there for!

And I am quite happy with the brand if isolator I use, MEM are tried and tested.
really? we have controls going through our isolators as well sometimes depending on spec
 
Having controls through a pole of an isolator sounds quite unusual.
Id expect to see control circuits use auxiliary contacts, but then I guess it depends on the equipment and budget.
 
It would be great if people learnt the difference between 3P+N and 4P. As Shanky rightly said in a 3P+N the neutral is early make late break. The reason, because you will get voltage imbalance akin to a floating neutral.




I’ve only ever specified four pole ACB/MCCB’s twice in 40 years.

Both breakers were for a 2.6MW 660V two wire earth free system. Four pole because I put two poles in series to handle the fault current. If you look at the manufacturer’s maximum fault current tables for 400V against 690V it drops dramatically!
 
It would be great if people learnt the difference between 3P+N and 4P. As Shanky rightly said in a 3P+N the neutral is early make late break. The reason, because you will get voltage imbalance akin to a floating neutral.
I’ve only ever specified four pole ACB/MCCB’s twice in 40 years.

Both breakers were for a 2.6MW 660V two wire earth free system. Four pole because I put two poles in series to handle the fault current. If you look at the manufacturer’s maximum fault current tables for 400V against 690V it drops dramatically!


Yep, all our 2.5-3.2 KA main switchboard TX ACB incomers and the bus couplings are 3 Pole + N with the early make late break function.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Swa main incomer size
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
27

Thread Tags

Advert

Thread statistics

Created
Mwoods4757,
Last reply from
davesparks,
Replies
27
Views
3,734

Advert