I know I have started another thread in the past with an almost identical title but this one is asking different questions!

The DNO are moving the meter box and I will need to extend the tails to approx 8m.

The present earthing arrangement is TT, I have asked the DNO to change to TN-C-S and they have said they will do so if they can.

I have 2 questions:

1. Would you always use SWA when extending the tails on a TT due to their not being any fault protection (assuming Ra>1ohm) or would tails be acceptable? I personally cant really see it being ok to run tails through the house (under floorboards) on a longer run as it quite significantly increases the risk of an accident happening.

2. If using SWA would it be better to use 3 core, or 2 core and run a separate earth? The reason for asking is mainly due to concerns about how easy the SWA is to manipulate when getting it to the CU. Is 2 core considerable easier than 3 core to manipulate or is there not a great deal of difference? It will be 16mm2 (80A switch fuse)

Cheers all.
 
use 3 core SWA. glanding into a metalclad CU should not pose any problems. obviously make sure the armour os earthed as well as using the 3rd core as cpc.
 
Regarding your point 1, I think it is a good one. I recently had a similar situation extending to a CU over a similar distance. The run was in a garage and could have theoretically been done in 25mm tails as it was all clipped direct from switch fuse to CU and mostly out of reach. However I decided to do it in SWA due to the environment, it just seems a more suitable selection method, and probably cheaper as well.
 
The armour is likely to be inadequate for bonding purposes whether TN-C-S or TN-S.
 
You've still got to have a sub distribution circuit now to feed the existing d.b/c.unit,any way you earth it be it core/swa sep.earth etc with switchfuse.(isolation & protection)
what are the earthing arrangements of other installations in the street will give a guide if PME exists etc.

If it still has to be TT you may have to fit a S type/time delayed RCD to acheive disconnection times for the distribution circuit.
 
  • Like
Reactions: sparksburnout
Yes it would apply to TN-S.
However the OP has not asked for the supply to be changed to TN-S.
 
Yes it would apply to TN-S.
However the OP has not asked for the supply to be changed to TN-S.
Point taken I read your post as a general comment.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SWA or tails?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
westward10,
Replies
9
Views
2,008

Advert