I will add a few points in addition to others concerns of exposed single insulated cables.

You tell us the supply is TN but what I was getting at is whether is is TNS or TNCS, this can matter, it may mean you garage requires equipotential bonding installed or isolation from electrical earth and rodding as a TT set up.
-Do you have a metal structure or support to the garage that is attached to the ground?
-Do you have any metallic pipes like service pipes (gas - water) coming up through the ground into the garage?

If the answer is yes to any of these questions then you may need to take specific measures in your earthing arrangements in the garage.
To note here that this will not be a concern if the garage is structurally part of the house and not a separate entity away from the house itself.
 
I will add a few points in addition to others concerns of exposed single insulated cables.

You tell us the supply is TN but what I was getting at is whether is is TNS or TNCS, this can matter, it may mean you garage requires equipotential bonding installed or isolation from electrical earth and rodding as a TT set up.
-Do you have a metal structure or support to the garage that is attached to the ground?
-Do you have any metallic pipes like service pipes (gas - water) coming up through the ground into the garage?

If the answer is yes to any of these questions then you may need to take specific measures in your earthing arrangements in the garage.
To note here that this will not be a concern if the garage is structurally part of the house and not a separate entity away from the house itself.
Hi

it is seperate at back of garden . No metalic structure /support to ground .
no metalic pipes only a plastic MDPE water pipe.

The electrician who did the intial 1st fix work didnt ask to get a steel rod on the shopping list he left me .So i am assusing that he is using the main earth supply via swa 3rd core

I will confirm with the electrcian when they come to energise and test the installation /supply as i dont have knowldge of testing and havent invested in the equipment yet .

Is there a way to distinguish between TNS or TNCS or is it only via testing ?

thanks
 
Confirm it with the Electrician, I didn't realise you were in tally with an electrician, don't worry about the supply characteristics then as this should have also been taken into account by your electrician, in hindsight it would have been better to get them in to do the extended joint as in its present state it would not comply as others have mentioned.
 
  • Like
Reactions: DPG and user786786
The CPC and neutral are connected to the same block of brass in the DNO service head on a TNCS system, so any Ze you measure at the CU will be just the resistance of the two tails, which for a 'normal' set up will be very close to zero.
On a TNS system, the connection point between the two is further back the line, so you should be able to measure a significant resistance.
 
  • Like
Reactions: user786786

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA too short !
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
user786786,
Last reply from
brianmoooore,
Replies
46
Views
8,320

Advert